I'll quite happily experiment with this - however if you could give me a 
short-cut to the relevant part of the code that would be appreciated as no 
doubt you are way more familiar with it than me.

Thanks, Tim.

On 25/09/2011, at 7:29 , Charles Lepple wrote:

> On Sat, Sep 24, 2011 at 5:00 PM, Tim Gould <tgo...@reverb.com.au> wrote:
>> -DDD output attached.
> 
> Given that the ConfigVoltage should not change for a given UPS, this
> should be useful:
> 
>   0.413040    Report[get]: (3 bytes) => 1d 11 01
>   0.413075    Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID:
> 0x1d, Offset: 0, Size: 16, Value: 2.73e-06
>   0.417039    Report[get]: (3 bytes) => 1f 18 00
>   0.417063    Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
> ReportID: 0x1f, Offset: 0, Size: 16, Value: 2.4e-07
>   0.421044    Report[get]: (2 bytes) => 07 0d
>   0.421080    Path: UPS.PowerSummary.PresentStatus.Charging, Type:
> Feature, ReportID: 0x07, Offset: 0, Size: 1, Value: 1e-07
>   0.421096    Report[buf]: (2 bytes) => 07 0d
> 
> If you multiply those values by 1e7, they should all be right. It
> looks like a misplaced exponent in the HID descriptor.
> 
> -- 
> - Charles Lepple
> 