Hi, Charles!

>
>> However, it seemed that the APC UPS is not recognized by usbhid-ups as long 
>> as the Cyper-power UPS is also plugged to the same system. Is that behavior 
>> correct?
>
>usbhid-ups will try to connect to the first PDC HID UPS that it finds, but if 
>the CyberPower UPS prevents either UPS from being recognized, then no, that's 
>not expected.

Situation 1:
Step 1: APC UPS plugged
Step 2: Cyber-power UPS pluged
Step 3: upsdrvctl start, Cyper-power UPS recognized

Situation2:
Step 1: APC UPS plugged
Step 2: upsdrvctl start, APC UPS recognized
Step 3: upsdrvctl stop
Step 4: Cyber-power UPS pluged
Step 5: upsdrvctl start, Cyper-power UPS recognized


Situation3:
Step 1: Cyber-power UPS plugged
Step 2: upsdrvctl start, Cyber-power UPS recognized
Step 3: upsdrvctl stop
Step 4: APC UPS pluged
Step 5: upsdrvctl start, Cyper-power UPS recognized

I check /proc/bus/usb/device, the cyper-ups is always ahead of the UPS one if 
thay are all plugged.

That comes another question: If two UPS device with different driver plugged, 
and the two drivers are both configured, are they both recognized?

 >
>You can used the vendorid or productid parameters (see 'man usbhid-ups' or 
>docs/man/usbhid-ups.txt) to point usbhid-ups to one or the other.
>
I have only read of information of upsd pointed from User Manual. I will read 
and learn more about that.
>

--
Andrew Chang
2012-03-11
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to