Hello Denis,

There is no bug in what you are describing. NUT drivers are designed to kill 
themselves if they can not connect to their UPS device after their 
initialization.
The behavior is the same on UNIX and Windows : at service start-up, all 
configured drivers are started, if they do not find their UPS, they die and are 
never automatically restarted. It leaves you with upsd, upsmon and the drivers 
which have successfully connected to their UPS.
So the rule is: your hardware must be up and running before starting NUT.

Regards,
Fred

--
Eaton Opensource Team - http://opensource.eaton.com



-----------------------------

-----------------------------

________________________________________
From: nut-upsuser-bounces+fredericbohe=eaton....@lists.alioth.debian.org 
[nut-upsuser-bounces+fredericbohe=eaton....@lists.alioth.debian.org] on behalf 
of Denis Serov [[email protected]]
Sent: Tuesday, September 11, 2012 7:18 PM
To: [email protected]
Subject: [Nut-upsuser] Back UPS ES and data stale with disconnected device

Hello NUT Team!

I continue playing with NUT for Windows and USBHID-UPS driver I've got from 
Frederic to fix "Data Stale" problem.

It seems there is something wrong when Network UPS Tools service is starting 
with disconnected USB cable. UPSMON is writing "Data Stale" to output  and 
continue do it infinitely, even the cable is connected back. Here is a short 
log:

Network UPS Tools upsmon 2.6.5-3691:3709M
   0.000000     UPS: [email protected] (master) (power value 1)
   0.015600     Using power down flag file C:\killpower
   0.015600     debug level is '5'
   0.015600     Trying to connect to UPS [[email protected]]
   0.031200     Login on UPS [[email protected]] failed - got [ERR 
ACCESS-DENIED]
   0.031200     Current power value: 1
   0.046800     Minimum power value: 1
   5.054409     pollups: [email protected]
   5.054409     get_var: [email protected] / status
   5.054409     Poll UPS [[email protected]] failed - Data stale
   5.070009     do_notify: ntype 0x0005 (COMMBAD)
   5.070009     Communications with UPS [email protected] lost
   5.085609     Current power value: 1
   5.085609     Minimum power value: 1
  10.097895     pollups: [email protected]
  10.097895     get_var: [email protected] / status
  10.097895     Poll UPS [[email protected]] failed - Data stale
  10.113495     do_notify: ntype 0x0008 (NOCOMM)
  10.113495     UPS [email protected] is unavailable
  10.129095     Current power value: 1
  10.129095     Minimum power value: 1
  15.134979     pollups: [email protected]
  15.134979     get_var: [email protected] / status
  15.134979     Poll UPS [[email protected]] failed - Data stale
  15.150579     Current power value: 1
  15.150579     Minimum power value: 1
  20.158188     pollups: [email protected]
  20.158188     get_var: [email protected] / status
  20.158188     Poll UPS [[email protected]] failed - Data stale
   ...

But if the cable is already connected when the service is starting, it catches 
COMMBAD (cable disconnected) and COMMOK (cable connected again) notifications:

Network UPS Tools upsmon 2.6.5-3691:3709M
   0.000000     UPS: [email protected] (master) (power value 1)
   0.015600     Using power down flag file C:\killpower
   0.015600     debug level is '5'
   0.031200     Trying to connect to UPS [[email protected]]
   0.031200     Login on UPS [[email protected]] failed - got [ERR 
ACCESS-DENIED]
   0.046800     Current power value: 1
   0.046800     Minimum power value: 1
   5.054409     pollups: [email protected]
   5.054409     get_var: [email protected] / status
   5.054409     parse_status: [OL]
   5.070009     parsing: [OL]
   5.070009     ups_on_line: [email protected] (first time)
   5.070009     Current power value: 1
   5.085609     Minimum power value: 1
  10.093218     pollups: [email protected]
  10.093218     get_var: [email protected] / status
  10.093218     parse_status: [OL]
  10.108818     parsing: [OL]
  10.108818     ups_on_line: [email protected] (no change)
  10.108818     Current power value: 1
  10.124418     Minimum power value: 1
  15.125250     pollups: [email protected]
  15.130250     get_var: [email protected] / status
  15.136251     parse_status: [OL]
  15.140251     parsing: [OL]
  15.143251     ups_on_line: [email protected] (no change)
  15.151252     Current power value: 1
  15.155252     Minimum power value: 1
  20.164865     pollups: [email protected]
  20.164865     get_var: [email protected] / status
  20.164865     Poll UPS [[email protected]] failed - Data stale
  20.180465     do_notify: ntype 0x0005 (COMMBAD)
  20.180465     Communications with UPS [email protected] lost
  20.196065     Current power value: 1
  20.196065     Minimum power value: 1
  25.211951     pollups: [email protected]
  25.211951     get_var: [email protected] / status
  25.211951     Poll UPS [[email protected]] failed - Data stale
  25.227551     Current power value: 1
  25.227551     Minimum power value: 1
  30.236992     pollups: [email protected]
  30.236992     get_var: [email protected] / status
  30.236992     parse_status: [OL]
  30.252592     do_notify: ntype 0x0004 (COMMOK)
  30.252592     Communications with UPS [email protected] established
  30.268192     parsing: [OL]
  30.268192     ups_on_line: [email protected] (no change)
  30.268192     Current power value: 1
  30.268192     Minimum power value: 1
  ...

Operating system is Windows 7 x64.

I can send additional logs if it is necessary...

Thanks,
Denis



_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to