On Fri, 26 Oct 2012, Kris Jordan wrote:
Did you install NUT from a package? Note, 2.6.5 is the current
version and 2.6.4 had fixed a vulnerability.
I'm using the nut 2.6.3 package included in the openSUSE 12.2
distribution.
Check that your distribution's shutdown script is running
'upsdrvctl shutdown' in the presence of the killpower file
(POWERDOWNFLAG).
Summary: looks like an openSUSE bug, simple fix available.
OpenSUSE 12.2 has a script /usr/sbin/rcupsd for starting and stopping the
upsd service. This is a link to script /etc/init.d/upsd which contains:
powerdown)
## Special command: Instruct UPS to shutdown.
sync &
if grep -q '^\[' $UPS_CONFIG ; then
echo -n "Instructing UPS to powerdown "
$UPSDRVCTL_BIN shutdown >/dev/null 2>&1 || rc_failed
rc_check
else
echo "No local UPS defined, skipping powerdown "
fi
rc_status -v
;;
try-powerdown)
## Special command: Instruct UPS to shutdown, if halt is running
## or variable UPSD_POWERDOWN_CONDITION is set and power is failing.
## Otherwise silently quit.
##
if test "$RUNLEVEL" = "0" -o -n "$UPSD_POWERDOWN_CONDITION" ; then
if test -n "$POWERDOWNFLAG" -a -f "$POWERDOWNFLAG" ; then
exec $0 powerdown
fi
fi
;;
where UPSDRVCTL_BIN=/usr/lib/ups/driver/upsdrvctl
In addition, file /etc/sysconfig/shutdown contains the configuration
parameter
# Hook during system shutdown to run extra command
HALT_POWERDOWN_INSERT="/etc/init.d/upsd try-powerdown"
but when upsd try-powerdown is called it fails silently because $RUNLEVEL
and $UPSD_POWERDOWN_CONDITION are empty. upsd powerdown is never called.
I changed the configuration parameter to
HALT_POWERDOWN_INSERT="/etc/init.d/upsd powerdown", reran command
SuSEconfig, and tried again but there was no change. However typing the
command /etc/init.d/upsd powerdown does shut down the UPS unit.
OpenSUSE 12.2 has fully embraced systemctl and systemd: I tried grepping
around in the /lib/systemd shutdown specifications, but I cannot find any
reference to /etc/init.d/upsd powerdown. This is beginning to look like a
bug in openSUSE 12.2 which I will report in their forums.
Here is a fix: There is a file /etc/init.d/halt.local which is currently
empty:
# /etc/init.d/halt.local
# script with local commands to be executed from init on system shutdown
# Here you should add things, that should happen directly before shuting
# down.
I added the lines
# RP 2012-10-28 Turn off the UPS unit.
# Needed for automatic system restart when wall power returns.
UPSDRVCTL_BIN=/usr/lib/ups/driver/upsdrvctl
echo `date -I` `date +%T` "$0 calls $UPSDRVCTL_BIN shutdown" >>
/var/log/halt.local
$UPSDRVCTL_BIN shutdown
I pulled the plug from the wall and witnessed a server shutdown followed
10 seconds later by a UPS shutdown. Pushing the plug back into the wall
got the system running again.
Roger
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser