Hello, Roger.

...if main power comes back within 10 seconds after the UPS has been
shut down, the UPS will power up the PC but the latter will not start.

.... You can change the parameter ups.delay.start into your UPS to set
the "Interval to wait before (re)starting the load (seconds)"
use upsset to change the value.

Hi, You could also place a declaration such as

   ondelay = 60

in file ups.conf.

I am afraid the ondelay argument only has effect when main power returns *before* UPS shutdown. The following is an excerpt from the man page for usbhid-ups (the driver for MGE Protection Center 675):

Set the timer for the UPS to switch on in case the power returns after the kill power command had been sent but before the actual switch off.

Besides, I have already tried increasing ondelay but to no avail.

Regards:
Angel