On Nov 8, 2014, at 1:52 PM, Steve Read <sd_r...@hotmail.com> wrote:

> I have made changes but it is still the same. That is when the server gets 
> the lowbat/noAC signal it does shut down as expected but the slave does not. 
> 
> Perhaps it makes sense for me to list the present settings:
> 
> On the Master:
> 
>      nut.conf
>         MODE=netserver
> 
>      ups.conf
>        [sdrups]
>            driver = genericups
>            port = /dev/ttyS1
>            desc = "For Server & Backup"
>            upstype=9
> 
>      upsd.conf
>         LISTEN 0.0.0.0
> 
>      upsd.users
>          [root]
>            password  = mypassword
>            upsmon master
>            instcmds = ALL
> 
>      upsmon.conf
>         MONITOR root@192.168.0.7 1 sdrups autocadba2 master

This looks good, except for the MONITOR line. Given the above settings, I think 
you need this:

MONITOR sdrups@192.168.0.7 1 root mypassword master

> 
> On the Slave:
> 
>      nut.conf
>         MODE=netserver

MODE=netclient for the slave.

>      upsmon.conf
>         MONITOR root@192.168.0.7 1 sdrups autocadba2 slave

Same username/password change as above:

MONITOR sdrups@192.168.0.7 1 root mypassword slave

> Master: 192.168.0.7
> Slave:   192.168.0.6
> 
> Dealing with the firewall I applied the following to both the master and 
> slave:
> 
>    sudo iptables -A INPUT -p tcp --dport 3493 -j ACCEPT
> 
> 
> I have looked in the log files but have not seen anything to suggest a 
> problem.

You should see something like this in /var/log/daemon.log:

upsmon[1234]: Communications with UPS sdrups@192.168.0.7 established

And something like this from netstat on the slave:

$ netstat -t |grep -w nut
tcp        0      0 192.168.0.6:40925       192.168.0.7:nut  ESTABLISHED


-- 
Charles Lepple
clepple@gmail



_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to