On 03/04/17 22.11, Gene Heskett wrote:
On Monday 03 April 2017 14:13:08 Stuart D. Gathman wrote:
Back on the mailing list, where such belongs.
[cuuut]
We want the ALARM that the nut driver is
generating, and upsd is passing on - to be acted on in some way by
upsmon. Which NOTIFYCMD is run when there is an ALARM?
[cuuut]
I dont think any NOTIFYCMD is run when there is an ALARM Stuart.
I've not read the docs in ages, but if there isn't something mentioned in
a man upsmon, I would be unpleasantly surprised.
According to my copy, it does a -wall (warn all) by default, and it looks
like REPLBATT is one such message, and the default time for a repeat is
12 hours. The -wall type message shows on every open terminal on the
system's network, so someone should see it. From the upsmon.conf file:
[cuuuut]
Possible values for type:
ONLINE
UPS is back online
ONBATT
UPS is on battery
LOWBATT
UPS is on battery and has a low battery (is critical)
FSD
UPS is being shutdown by the master (FSD = "Forced
Shutdown")
COMMOK
Communications established with the UPS
COMMBAD
Communications lost to the UPS
SHUTDOWN
The system is being shutdown
REPLBATT
The UPS battery is bad and needs to be replaced
NOCOMM
A UPS is unavailable (can’t be contacted for monitoring)
ALARM is not mentioned, so I suppose NUT only reacts to the Online message it
gets?
JonB