Thanks a lot, I will do it and keep you informed. Best regards Andrea
2017-06-12 12:34 GMT+02:00 Manuel Wolfshant <wo...@nobugconsulting.ro>: > On 06/12/2017 12:56 PM, Andrea de Lutti wrote: > > > >> > I have also successfully tested the battery... >> > >> > upscmd -uadmin -pups Elit@artu test.battery.start.quick >> >> I would also recommend testing the shutdown procedure and making sure >> that everything works as expected on power failures. >> Please, let us know the results of these tests, so that we can add a >> more informed report about your device to our library >> (http://networkupstools.org/ddl/). >> > > Nice, I would like to test it, but if I don't have battery runtime value > and / or battery charge, how may I test it correctly? > I have seen also some strange values for battery.voltage.high and > battery.voltage.low....are they correct? > > run with a test load ( at least twice, for 50% and 100% load for > instance ) and write down the periods between full charge and shutdown. > Then you can use runtimecal in ups.conf to obtain guestimations during > normal usage >
_______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser