Most important thing: Portable generators are made in two different ways: An
isolated neutral and a bonded neutral. If your not using a transfer switch you
need to have the neutral bonded to the following things: ground (that means a
grounding electrode, and a grounding electrode conductor), the frame of the
generator, and the equipment grounding conductor.
Without those connections the safety of your setup will be severely
compromised.
(Most portable generators have that all wired internally, except for the
grounding electrode which, if the use of the generator is temporary, I think
your allowed to skip it.)
Again, GLHF!
Josiah Luscher.
On November 15, 2014 10:49:38 AM PST, Josiah Luscher <[email protected]>
wrote:
>I'm an Electrician, but I don't necessarily have all the answers.
>
[SNIP]
>
>If you want really clean power get all four: Isolation transformer, a
>surge supressor, a high precision line reactor, and a UPS. Each does a
>slightly different thing. But that might be overkill.
>
>I renovated a high school once where the engineer must have felt that
>they had dirty power (near a sub station possibly). He specified
>isolation transformers and line reactors for every VFD in their HVAC
>system. It was pretty cool to work with that stuff.
>
>Good luck!
> Josiah Luscher
> ( OR: 26166J - WA: LUSCHJJ861B9 - UT: 6753759-5504)
>
>
>On November 15, 2014 9:29:17 AM PST, Chuck Hast <[email protected]>
>wrote:
>>Based on your description of the problem, looks like you
>>need a "On line double conversion UPS",
>>
>[Cut out for brevity, I hope that's not rude]
>>
>>
>>
>>On Thu, Nov 13, 2014 at 5:36 PM, jim karlock <[email protected]>
>>wrote:
>>
>>> Not all UPS reform the sine wave. ALL of the low cost ones I have
>>> played with merely pass through the line, then switch to internal
>>> power when the line goes away.
>>>
>>> My main worry would be over voltage. Get a voltmeter!
>>>
>>> PS: None of those low cost UPS, that I played with, put out a sine
>>> wave - they put out a "modified sine wave" which has a zero volts
>>> time to allow a peak voltage the same as a sine wave, with a RMS the
>>> same as a sine wave:
>>>
>>> --- --- --- ---
>>> | | | | | | | |
>>> - - - - - - - -
>>> | | | | | |
>>> --- --- ---
>>> thanks
>>> JK
>>>
>>>
>>> At 05:15 PM 11/13/2014, David wrote:
>>> >On 11/12/2014 09:45 PM, John Jason Jordan wrote:
>>> >
>>> >< lots of stuff clipped >
>>> >
>>> > > Do I need to be concerned? If so, what kind of line conditioning
>>> > > equipment shuld I use?
>>> > >
>>> >
>>> >I am not an electrician nor do I have a lot of experience with
>this,
>>but
>>> >I think you would be safe with any of the reasonably priced UPS
>>devices
>>> >on the market as an intermediary.
>>> >
>>> >The UPS should help to reform the sine wave, hence conditioning,
>the
>>> >incoming signal from the wall to keep your equipment happy, and
>>provide
>>> >a bit of protection from surges as well.
>>> >
>>> >I've read that damage to electronics is caused more by brownouts
>>than
>>> >surges, so in addition to being able to keep the devices up and
>>running
>>> >(presuming no built-in batteries) during the switch from one outlet
>>to
>>> >the other, the UPS will hopefully prolong the life of your
>equipment
>>as
>>> >well.
>>> >
>>> >david
>>> >_______________________________________________
>>> >PLUG mailing list
>>> >[email protected]
>>> >http://lists.pdxlinux.org/mailman/listinfo/plug
>>> _______________________________________________
>>> PLUG mailing list
>>> [email protected]
>>> http://lists.pdxlinux.org/mailman/listinfo/plug
>>>
>
>--
>Sent from my Android device with K-9 Mail. Please excuse my brevity.
>_______________________________________________
>PLUG mailing list
>[email protected]
>http://lists.pdxlinux.org/mailman/listinfo/plug
--
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
PLUG mailing list
[email protected]
http://lists.pdxlinux.org/mailman/listinfo/plug