Duke response is similar to Tom Meek's.

What are your FSAR limits (dose rates or concentration levels), and how did you 
come up with these numbers?

The general basis for acceptance of radioactivity concentrations in outdoor 
liquid holdup tanks is to show that postulated failure of the tank and its 
associated components would not result in radionuclide concentrations in excess 
of 10 CFR Part 20, Appendix B, Table 2, Column 2 at the nearest potable water 
supply in an unrestricted area.

What is your process to monitor these tanks to make sure you comply with your 
FSAR requirements?

Compliance is demonstrated by monthly sample analysis.

Thanks,

[cid:[email protected]]

Senior Engineer, PE
Corporate Radiation Protection
Nuclear Generation Department
Duke Energy Carolinas
(704) 382-4496

From: [email protected] [mailto:[email protected]] On Behalf Of 
SCHLAPKOHL, DANIEL
Sent: Wednesday, September 21, 2011 6:06 PM
To: [email protected]
Subject: RE: Powernet: FSAR requirements

Your right Tom. You are the only one to answer my request. Thanks for replying.


Dan Schlapkohl

Supervisor, Radiological Operations

Grand Gulf Nuclear Station

601-437-6189

[email protected]

________________________________
From: [email protected] [mailto:[email protected]] On Behalf Of 
Orionhp
Sent: Wednesday, September 21, 2011 9:12 AM
To: [email protected]
Subject: Re: Powernet: FSAR requirements

I noticed that you have not gotten any responses to this question.  My answers 
are given below.  They apply to the now decommissioned Trojan reactor located 
in Oregon.
Tom Meek

On 9/7/2011 11:16 AM, SCHLAPKOHL, DANIEL wrote:

I have an action to change our FSAR for stored radioactivity in our CST and 
RWST tanks outside of the RCA. We currently have 0.5 and 10 mR/hr contact dose 
rate limits on these tanks. I would like to know the following;



What are your FSAR limits (dose rates or concentration levels), and how did you 
come up with these numbers?
            The FSAR limits were concentration of radioactive material based on 
the dose to a member of the public from drinking water downstream from the 
plant from the total release of the tank                 contents due to a 
rupture.  The dose limit to the public was used to back calculate the maximum 
concentration based on minimal dilution.


What is your process to monitor these tanks to make sure you comply with your 
FSAR requirements?
            There were no process monitors.  A sample was collected for 
analysis by chemistry.



 Thanks for your help,



Dan Schlapkohl

Supervisor, Radiological Operations

Grand Gulf Nuclear Station

601-437-6189

[email protected]<mailto:[email protected]>

<<inline: image001.jpg>>

Reply via email to