Response from Diablo Canyon.

From: Miller, Clint
Sent: Tuesday, February 05, 2013 9:27 AM
To: [email protected]
Cc: [email protected]
Subject: Powernet: RCS Filters
Importance: High

Douglas,
   At Diablo Canyon we currently use 0.1u absolute pore size filters in RCS 
letdown, Seal Water injection and Seal water Return filter vessels.

  Originally our plant had 25u nominal filters in these vessels except Seal 
Water Injection which was 5u Nominal. We reduced pore size one step at a time 
to prevent overwhelming radwaste with high activity filters they could not 
handle, store, process or ship.  A smaller size filter would be installed in a 
vessel and if it didn't D/P in 3 months we stepped down another pore size. Our 
results were that we could have jumped from the course pore size down to 2u in 
one step.
  Going below 2u we did generate more filters. If you are not using macroporous 
(filtration) resin in your shut down clean up bed, you will likely mimic our 
experience.  As we stepped down from 2u to 1u we had several filters D/P before 
3 months had passed. Only after getting a 3 month run did we down size to 0.45u 
and then to 0.1u.
  I'd suggest you obtain a spent filter transfer cask, if you don't have one 
already and line up a filter HIC or shielded drums so that radwaste has a place 
to put spent filters should they D/P quickly. We had our fix it now team 
assigned to replace the filters and procedures in place for each vessel prior 
to ever stepping down a filter pore size.
  If you have use the macroporous resins [Purolite 501P, 5070 or PRC 0-1] in 
CVCS, you might be able to step down from 2u to 1u with no added filter 
generation.
  We did find that once we reduced size below 1u we started seeing C-14 in the 
off-site Lab filter samples. In order to limit Greater than Class C generation 
the submicron filters might have to be removed prior to D/P to limit the amount 
of C-14 on the filters.

 Good Luck,
  Clint Miller
805-545-4582


________________________________
From: Sewell, Linda
Sent: Tuesday, February 05, 2013 8:53 AM
To: Miller, Clint
Subject: FW: Powernet: RCS Filters
Importance: High
Hi Clint,

Can you answer this.  I will forward on.

Linda


From: [email protected]<mailto:[email protected]> 
[mailto:[email protected]] On Behalf Of 
[email protected]<mailto:[email protected]>
Sent: Tuesday, February 05, 2013 7:57 AM
To: [email protected]<mailto:[email protected]>
Subject: Powernet: RCS Filters
Importance: High

Davis-Besse is considering lowering the micron size of the RCS letdown filter 
from 2 micron to 1 microns.  Requesting  industry information regarding the 
micron size  of RCS filters used at your station (on-line).

Thanks

Douglas L. Noble
Manager - Radiation Protection
Davis-Besse Nuclear Power Station
(419) 321-7780 office
(419) 304-0068  cell
----------------------------------------- The information contained in this 
message is intended only for the personal and confidential use of the 
recipient(s) named above. If the reader of this message is not the intended 
recipient or an agent responsible for delivering it to the intended recipient, 
you are hereby notified that you have received this document in error and that 
any review, dissemination, distribution, or copying of this message is strictly 
prohibited. If you have received this communication in error, please notify us 
immediately, and delete the original message.


PG&E is committed to protecting our customers' privacy. 
To learn more, please visit http://www.pge.com/about/company/privacy/customer/

Reply via email to