Hi Larry,
Did this occur even if there were other loads on?
jay
peltz power
On Jun 18, 2009, at 7:39 PM, Larry Crutcher, Starlight Solar wrote:
Hi Jeff,
I am not sure if this relates to your issue but there is an issue
with Magnum inverters and Splindide washers. Splindide will not work
on a Magnum sine wave. They are aware of this. Here is a copy of my
old post to the list:
....I have a recent power issue come up with a Magnum inverter. A
customer tried to operate her Splindide washer/dryer but the motor
would not start. I looked at the waveform with a scope and RMS
voltage and frequency were fine. The waveform looked good until the
motor tried to start. The washer was putting a jagged noise riding
on the sine wave. The voltage and waveform still looked OK other
than the noise. I was mostly sure that this was the cause so I
grabbed a 600 watt cheap import sine wave inverter and connected the
washer. Same ripple was present on the waveform but the $400
inverter would run the washer motor fine. It also runs fine with a
1600 watt Honda inverter/generator.
Larry Crutcher
Starlight Solar
(928) 941-1660
Renewable Energy Products, Service and Installation
On Jun 18, 2009, at 4:44 PM, Jeff Oldham wrote:
Not sure if anyone offered this already - The DR will do a 5 sec.
surge to 6200W the Outback will do a 5 sec. surge to 4800W. This is
common, most mod's will surge considerable more than Sine's, that
is the big trade off other than power quality and tare losses. In
addition I'm very skeptical that the Staber only surges to 11A,
have you measured the actual surge? When I replaced my good 'ol
Trace 2512 (too many appliances disliked the mod. sine) and went to
a Magnum 2812 my washer would kick it out as my washer surged to
31A and the Mag. would do 30! This is a modern Horz. axis machine.
I now have the Magnum and a new Vanner ITC 12-3200W that does a 3
sec. surge to 6400W and will even run my wire welder and air
compressor, both used to be genny only loads.
-jeff o
From the Solar, Wind and Hydro powered office of Jeff Oldham/
Regenerative SOLutions
____________________________________________________________
Save on Moving Supplies. Click Here!
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org