All -

PVC doesn't hold up well in the Bay Area - Here's a photo of  some ~4 year old 
PVC browned PVC from Marin County:

[cid:image002.jpg@01CA48DF.F8EAE150]

You can see that the straps melted resulting in the conduit sliding down. Thank 
goodness we didn't install this. PCV seems like a good option for shaded areas.

As Bill pointed out, if we use EMT we need to bond both ends of the conduit to 
comply with NEC 250.97. My issue is that it is hard to find outdoor rated 
bonding bushings - that's why we've just been installing cast metal boxes with 
threaded connections (complies with NEC 250.92(B)(2)).

As William point out, EMT is robust and reliable. I still think that there must 
be more efficient way to go between arrays. Maybe that's why commercial low 
profile racking systems are often fully integrated systems with built in wire 
raceways.

-August


August Goers

Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
aug...@luminalt.com

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Friday, October 09, 2009 12:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

Ray:

Good question.  We do use PVC in coastal zones to avoid corrosion.  We try to 
keep it in the shade, paint it where exposed to UV and support it in close 
intervals.

William


At 10:57 AM 10/9/2009, you wrote:

Except for coastal installations.... where  EMT is NOT  recommended outdoors, 
PVC browns out and warps, and we should therefore use product X???

R. Walters
r...@solarray.com<mailto:r...@solarray.com>
Solar Engineer




On Oct 9, 2009, at 11:38 AM, William Miller wrote:


August:

I suggest the use of EMT with proper fittings to protect high voltage, high 
amperage DC Wiring on rooftops.  Sure it is time consuming, but high quality, 
reliable craftsmanship will always be thus.

William Miller



<<inline: image002.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to