I got into that one a few years ago with an inspector. He cited 110.2. "Approved" according to article 100 means: acceptable to the AHJ. So put article 100 into 110.2 and you get: "Conductors and Equipment required or permitted shall be acceptable only if 'acceptable to the AHJ' "
Basically I call these 2 sections of the code read together as the 'AHJ = The Man' ruling. I guess there was some politics involved in NOT putting that together for all to see? R. Walters r...@solarray.com Solar Engineer On Jan 11, 2010, at 5:27 PM, Kent Osterberg wrote: > David, > > The NEC doesn't require UL listing. The most appropriate section of the code > about this is Article 110, Requirements for Electrical Installations, it > requires equipment to be approved. _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org