Once I have fulfilled NEC min. requirements, I use a spreadsheet to analyze the 
cost of larger wire vs. the cost of power lost. Going under 2% is usually not 
worth it, if copper prices are high, and PV cost is low enough (current 
market). Sizing for under 2% was good economics a few years back, when PV was 
high, and copper was low, though.

For NEC 2011, I agree: while I readily welcome development of DC AFI, 
implementing code before the technology is ready, is a bad idea. But that may 
be the only way to get the technology in place.....

Ray

On Apr 6, 2010, at 11:15 AM, Kent Osterberg wrote:

> Ray,
> 
> Considering that we design PV wiring to be efficient with voltage (and power) 
> loss typically less than 2%, the wire size is nearly irrelevant to arcing 
> issues.   Essentially all the energy available from the PV array can be 
> dissipated in the dc arc.   And since the current is limited by the nature of 
> the IV curve, breakers alone usually won't clear the fault.  The best 
> combiner breakers can do (if you have enough parallel circuits) is isolate 
> the fault to one string in the PV array.  With one string being 1 or 2 kW in 
> many systems there is still the potential for a lot of heat.
> 
> With the 2011 code just around the corner and no dc arc fault protection on 
> the horizon, it looks like our industry is again going to have a code 
> requirement that no one can fulfill.  
> 
> Kent Osterberg
> Blue Mountain Solar, Inc.
> 
> 
> 
> R Ray Walters wrote:
>> 
>> I agree that we don't want to create the code first, and try and develop the 
>> product after. On the other hand, if a DC AFI can be developed that could 
>> stop some of the problems I've seen breakers not help, I'm installing them, 
>> and pushing for code requirements.
>> AC GFIs were gimmicky too at first, but now have gone on to save countless 
>> lives; usually kids, but a few of us wet booted contractors too.
>> As far as running things at 100%, I do agree with you, but I also think that 
>> 156% over rating in many cases is too much. If the wire and breaker are that 
>> oversized, it is less likely to trip when you want it to. 
>> My most recent damage I saw, the cable a few inches back was in no way 
>> damaged, as it only saw array short circuit current, but the connector that 
>> arced burned up a whole circuit board.
>> More oversizing would have only increased the arc potential, and reduced  
>> the chances of a breaker tripping.
>> Proper sizing (not too big, not too small) is the way.
>> 
>> R. Walters
>> r...@solarray.com
>> Solar Engineer
>> 
>> 
>> 
>> 
>> On Apr 6, 2010, at 9:16 AM, robert ellison wrote:
>> 
>>> I have seen info from independent tests that convinces me that AFCI's 
>>> probably don't work for AC and i hate to think what they would do for DC, 
>>> if anything. Besides drive the costs up.
>>> This was a few years ago and maybe they have gotten it together by now.
>>>  
>>> Anyone remember the original ground faults form Trace (?) after the code 
>>> change requiring them in 96? Expensive and prone to catching fire comes to 
>>> mind, if i remember correctly. Lets not encourage more if that type of 
>>> experimentation in the industry.
>>>  
>>> Just the same i am not a believer of running anything at 100%, it will 
>>> always have a higher failure rate than something run at a lower capacity, 
>>> be it a generator, lawn mower or a circuit breaker.
>>>  
>>> Bob
>>>  
>>>  
>>>  
>>>  Mon, Apr 5, 2010 at 5:36 PM, William Miller <will...@millersolar.com> 
>>> wrote:
>>> Ray:
>>> 
>>> It is my analysis that combiner breakers (if present) will protect only 
>>> wiring upstream of the combiner -- that is, the individual string circuits. 
>>>  This protection would happen if there is a fault in one individual string 
>>> (in the wiring or the modules) that allows current from other strings, in 
>>> excess of the breaker rating, to be supplied through the breaker feeding 
>>> the faulted string.
>>> 
>>> There are two scenarios at play here:
>>> 
>>> 1.  Any fault between the combiner and the feeder destination will not trip 
>>> any circuit breakers.  The breakers are sized such that the current from 
>>> each individual string is less than the breaker rating (by more than 1.56 
>>> times) and they will not open.
>>> 
>>> 2.  PV GFDI protection at the destination end of a feeder will not help.  
>>> PV GFDI circuits will not remove power from a feeder and they will open the 
>>> ground-to-grounding conductor bond.
>>> 
>>> Analyzing this further:  Fault conditions are made more likely given that 
>>> PV string circuits are no longer protected by conduit.  Faults are then 
>>> more likely in individual string circuits (those circuits without conduit 
>>> protection).  This is most problematic at installations with two or fewer 
>>> strings, where there is no combiner, i.e. residential installations.  
>>> Statistically, residential installations offer greater exposure to 
>>> electrical fires because: occupancy occurs for more hours per year, fire 
>>> alarms and sprinklers are often not installed, children are more often 
>>> present and standards are more lenient for residential wiring systems.
>>> 
>>> These two facts are PVs dirty little secrets.  Further innovation is 
>>> needed...
>>> 
>>> William Miller
>>> 
>>> 
>>> 
>>> At 12:22 PM 4/5/2010, you wrote:
>>>> I think the 100% rating exception is an interpretation issue. I consider 
>>>> the assembly to be defined as the breaker mounted in its listed enclosure.
>>>> I agree that the AFIs would add cost, but they might actually offer some 
>>>> protection too. (possibly one AFI unit could offer protection for multiple 
>>>> circuits?)
>>>> I've never had a PV circuit breaker actually trip, except some nuisance 
>>>> tripping due to faulty breakers.
>>>> PV breakers seem to only offer protection for very limited situations ie, 
>>>> a short in a PV wire being backfed by enough other PV circuits to trip the 
>>>> breaker.
>>>> It could happen, but I've never actually seen it. Even completely 
>>>> shattered modules still have enough internal resistance to limit the short 
>>>> circuit current to
>>>> a value below the breaker trip point.
>>>> 
>>>> Ray
>>>> 
>>>> On Apr 4, 2010, at 11:47 PM, Kent Osterberg wrote:
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>>   
>> 
>> 
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com 
>> Version: 9.0.800 / Virus Database: 271.1.1/2794 - Release Date: 04/05/10 
>> 23:32:00
>> 
>>   
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org