Hi Dana, 

 

Sorry for the delay - been on the road.  Not sure if this has already been 
presented / discussed. 

 

The old standby from industrial chargers, is 100% SOC is reached when charge 
current drops to 2% of capacity (normaly based on 6 or 8 hr rate).  Please 
note, this comes from an era of constant voltage with 8 hrs to recharge then 
rest the batteries.  However, it is an accurate indication of full charge. 

 

Time for acid mixing?  Now that is a tough one!  GC2 & L16's would be close in 
30 mins or ~ 10 - 15 mins per 100AH once full charge has been attained however, 
not sure we can apply to larger format cells.    

 

Regards, 

 

Jamie 

>>> "Dana" <d...@solarwork.com> 7/21/2010 7:54 PM >>>

As the % of full charge is related to the of degree absorption & gravity [the 
denser & more charged acid descending, and lighter acid rising] @ what point in 
the absorption would be prudent to stop charging? 

  

I used to cut off the charge on the Trace SW series at 12 “return amps”, VS. 
the factory default I think was at 5 amps.  This has & continues to work well 
but I never had anyone really answer this function clearly. 

  

Is there a battery manufacturer  or wrench that would care to comment on the:   

The minimum “Return” amps to disconnect for a “full”  charge? 

OR 

The time required per 100 AHR after reaching the Absorption point setting for 
the mix to occur? 

  

I realize that battery construction, battery condition, age and temperature and 
the current power usage will also play into this factor and it may not be a 
simple answer. 

  

  

  

  

  

 Dana Orzel 

  

Great Solar Works, Inc 

E - d...@solarwork.com 

V - 970.626.5253 

F - 970.626.4140 

C - 970.209.4076 

web - www.solarwork.com 

Responsible Technologies for Responsible People since 1988" 

  

From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, July 21, 2010 4:25 PM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters 

  

Allen, 

  

Can I infer that if you are shutting off the gen before charge rates drop in 
absorption that you are running only briefly in the absorb phase? Or do your 
charge currents remain high through out an extended absortion phase? 

  

Perhaps you have plenty of PV which you rely upon to bring the batteries up 
through the absorption phase, once the gen is shut off. 

  

I would be interest to learn more about your approach to this. 

  

Thanks, 

 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  

  

  

  _____  

From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters 

The Onan RS20000 shown in the generators article in HP 131 page 98 has 
performed flawlessly as backup support to an Outback quad-stack of VFX3648s. 
Differences, however, are that this 20kW gennie charges four inverters, rather 
than two; the elevation is 6,600 feet for about a 20% output deration; there 
are no huge loads above charging draw; and the client is aware enough to shut 
it off before absorption reduces the charge rate - all different conditions 
than you have described, as the gennie is usually fully loaded and running in 
balance.

Darryl is right about the amount of words necessary. 

AllanSindelar
Allan <mailto:al...@positiveenergysolar.com> @positiveenergysolar.com 
<mailto:al...@positiveenergysolar.com> 
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3008 - Release Date: 07/21/10 
00:36:00 



This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content. 

The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^% 

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3023 - Release Date: 07/23/10 
00:36:00

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to