Because the ground is not fuse protected.  A short from the conduit to grounded 
frames and then to the "grounded" conductor passes through the comon "gronded 
conductor" bus to all of the modules in that string and all other strings that 
share that "grounded conductor bus"  which is probibly all the modules in the 
array.  
Darryl 

--- On Mon, 10/18/10, Nick Soleil <nicksoleilso...@yahoo.com> wrote:


From: Nick Soleil <nicksoleilso...@yahoo.com>
Subject: Re: [RE-wrenches] Target fire
To: gilliga...@gmail.com, "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Monday, October 18, 2010, 4:08 PM





Hi Matt:
    I saw you chimed in after I had sent my posting.  It appears that the fire 
was caused by just the one fault at the loose 2" EMT connector.  If one of the 
module strings was faulted, then the fuse protecting that one string should 
open, and thus eliminating that string from the array.  Why do you think that 
the module level wiring contributed?

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037






From: Matt Lafferty <gilliga...@gmail.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Mon, October 18, 2010 1:12:34 PM
Subject: Re: [RE-wrenches] Target fire


Andrew,
 
The General/Prime Contractor on the job was SunPower vis a vis Powerlight. As 
per standard operating procedures there, the actual installation was subbed 
out. I don't recall which subs they used on this job, but there was more than 
one. Per their normal routine, one sub installs the racking, modules, and 
wiring from the modules to the combiners. This sub can have any one of several 
different license classifications. They use an electrical sub to install the 
combiners, homeruns, inverters, interconnection. The electrical sub is 
responsible for terminations.
 
Although I wasn't onsite to inspect the charcoal, I believe there were multiple 
shorts, not just the separated coupling in the homerun. I suspect there was at 
least one ground-fault in the array prior to whatever happened at the coupling. 
If this was the case, then BOTH SUBCONTRACTORS FAILED. They are both at least 
partially responsible for what happened there.
 
I have seen the racking system that was used on the Bakersfield project. The 
vintage used there had SEVERE problems with wire management. Absolute crap! 
Ground faults are common with that racking system. I have personally witnessed 
a system running with 8 amps of current on the ground using the same racking 
system. This was NOT on the Bakersfield site. Although I wasn't permitted to 
troubleshoot the problem, I was told that they had been chasing the ghost for 
several months. Ever since the initial installation. I have it from reliable 
sources that this condition is common and a known flaw in the design. At that 
time, their philosophy was that a ground fault is acceptable as long as there 
isn't enough current to trip the inverter offline. Central inverters commonly 
have up to a 10 amp GFP, so you can have one or more strings directly shorted 
and keep running. 
 
The concept that they kept installing systems with a known flaw like this is 
beyond acceptable. SunPower ultimately bears the greatest share of 
responsibility here. I do not know whether they have corrected the crappy wire 
management in that racking system since then or not. I certainly hope they have 
either corrected it or stopped using the system altogether. 
 
A comprehensive commissioning process would identify these problems and prevent 
the system from being placed into service. A visual inspection is the beginning 
of any commissioning process. As I said, I have seen these systems and they 
ain't pretty. Any schmuck can easily see numerous wires pulled across 
sharp-edges of sheet metal at various points throughout the array. Fail #1. 
Megger output jumpers... Fail #2.
 
The concept that any building department has signed one of these systems off at 
all is mind-boggling. Another thing I find interesting... There was no mention 
of this condition in the fire investigation report. Only a recommendation to 
megger the remaining wires. What's up with that? How is it that so many of 
these systems have been installed and passed inspection? How many have caught 
fire that we haven't heard about? You know... Just a little fire.
 
I would LOVE to know how much downtime has been logged because of this 
dangerous problem. And how much money has been spent troubleshooting and 
"fixing" faults caused by this problem. And how many "technicians" have been 
shocked during installation or service? One thing I can guarantee you... Unless 
you work inside the bowels of SunPower or this information comes out in a 
lawsuit somewhere, we will never know. Maybe WikiLeaks will have something on 
this someday. But I'm not holding my breath.
 
For the record, I'm not a SunPower hater. I do hate crappy workmanship. I hate 
the practice of covering up crappy workmanship even more. You see, when you 
cover it up, it's just gonna keep happening. At least until somebody calls you 
on it.
 
$0.02001

Solar Janitor
 


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Andrew Truitt
Sent: Monday, October 18, 2010 12:04 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Target fire

Thanks William.  That is the first place I looked but I didn't see it in 
there.  But I love all the resources on your website!


- Andrew

On Mon, Oct 18, 2010 at 12:47 PM, William Miller <will...@millersolar.com> 
wrote:


Andrew:

It may be in the report:  http://mpandc.com/practices/Safety/safety_data.html

William 




At 11:30 AM 10/18/2010, you wrote:





Does anyone know who installed the infamous Bakersfield Target job?



Andrew Truitt
NABCEP Certified PV Installer™ (ID# 032407-66)
Truitt Renewable Energy Consulting
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713



"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to 
fission. And it just so happens that there's an enormous fusion reactor safely 
banked a few million miles from us. It delivers more than we could ever use in 
just about 8 minutes. And it's wireless!"

~William McDonough

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.448 / Virus Database: 271.1.1/3204 - Release Date: 10/18/10 
06:34:00
Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
____________________________________

Andrew Truitt
NABCEP Certified PV Installer™ (ID# 032407-66)
Truitt Renewable Energy Consulting
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713

"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to 
fission. And it just so happens that there's an enormous fusion reactor safely 
banked a few million miles from us. It delivers more than we could ever use in 
just about 8 minutes. And it's wireless!"

~William McDonough



-----Inline Attachment Follows-----


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to