I believe the issue we had has to do with using the Sanyo high voltage PV 
module. As Kent points out, we were operating the controller at the design 
limit. I don't believe it is suited to do that as we have other Morningstar 
MPPT controllers working fine for several years now with lower voltage PV 
modules. BTW, the MPPT failures were in systems that we designed and installed 
using the Sanyo's.

The main reason we started using this controller is for 12 volt systems with a 
single high voltage module. We use other controllers when the Voc is less than 
40 volts. Warren, are any of the 200 units you sold last year used with a 200 
watt Sanyo other high voltage PV module(s)? 

Larry
  ----- Original Message ----- 
  From: Warren Lauzon 
  To: RE-wrenches 
  Sent: Monday, January 24, 2011 11:05 AM
  Subject: Re: [RE-wrenches] 10A Charge / load controller


  All controllers have failures – most commonly due to user/installer errors. 
Of all the controllers we sell, Morningstar have been by far the most trouble 
free and has the best no-hassle warranty.

  We have probably sold/installed around 100 to 200 of the SS-MPPT-15 
controllers over the past year or so, and have seen almost zero problems that 
were not caused by a bad installation of some sort. Just on a side note, of all 
the controllers of all brands we have sold over the past decade, probably 3/4 
of those returned by end users as “not working” has nothing wrong with them.


  From: Kent Osterberg 
  Sent: Monday, January 24, 2011 10:39 AM
  To: RE-wrenches 
  Subject: Re: [RE-wrenches] 10A Charge / load controller

  The spec sheet for the SS-MPPT says 75 volts maximum open circuit.  Maximum 
PV power: 200 watts for 12-volt batteries and 400-watts for 24-volt batteries.  
While it is supposed to be protected from PV overload and PV high voltage, it 
doesn't seem surprising that failures that have been observed are in systems 
that are pushing on these limits.  Fortunately, Morningstar stands behind their 
product.

  Kent Osterberg
  Blue Mountain Solar, Inc.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org