See the FPN for NEC 300.7(B). You take the values in Table 352.44 and multiply by 0.2 for steel conduit. -Hans
_____ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Dickson Sent: Thursday, March 31, 2011 8:27 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Expansion joints Are there any usage charts to tell you when or how to use expansion joints in EMT? The NEC has one for PVC, but what do you refer to for EMT? Best regards, Mark Dickson, NABCEP Certified Solar PV Installer T Oasis Montana Inc. _____ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hans Frederickson Sent: Thursday, March 31, 2011 9:15 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Expansion joints We used an OZ-Gedney expansion coupling for 1-1/4" EMT on a recent job. The part # is TX-125 for 1-1/4", and it would be TX-150 for 1-1/2". It is the same as the OZ-Gedney AX expansion coupling for rigid conduit, but uses a rigid nipple and EMT connectors to adapt to EMT. The assembly is UL listed. -Hans _____ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Erika Weliczko Sent: Wednesday, March 30, 2011 5:54 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Expansion joints I recently used a Hubbell Killark product for rigid/IMC and was not happy with how the threads of the coupling engaged in factory conduit threads. Crousehinds XJG-EMT series is intended for EMT. And is described as being used indoors or outdoors. The EMT couplings mostly seem to be compression. REpower SOLUTIONS www.repowersolutions.com P: 216.268.2275 C: 216.402.4458 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jamie Johnson Sent: Tuesday, March 29, 2011 2:33 PM To: RE-wrenches Subject: [SPAM] Re: [RE-wrenches] Expansion joints Peter, Cooper makes one for 1.5" emt, not sure if it is rated for wet locations or not. part #XJG54 EMT, it allows for up to 4" max of conduit movement. Jamie Johnson NABCEP Certified PV Technical Sales Professional NABCEP Certified Solar PV Installer General Manager SOLAR POWER ELECTRIC -------- Original Message -------- Subject: [RE-wrenches] Expansion joints From: "Peter Parrish" <peter.parr...@calsolareng.com <http://peter.parr...@calsolareng.com%3e> >; Date: Tue, March 29, 2011 1:04 pm To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org> Does anyone have information (manu and part number) for expansion joints for 1-1/2 EMT? I have also heard that many EJs are designed for rigid conduit (RMC) and may not be directly applicable to EMT. - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert. 031806-26 peter.parr...@calsolareng.com Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885 _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
<<image001.jpg>>
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org