William, that was with the stacking cable in place. As you noted, without the stacking cable the neutral needs to be sized for double the ampacity due to lack of synchronization. However if the feeder is sized for a 35kW genset that might not be an issue.
This was on an SW, not a PS, but I'm pretty sure you'll see the same performance. The two had a lot of similarities at the core. Phil Undercuffler On Jul 28, 2011 1:54 PM, "William Miller" <will...@millersolar.com> wrote:
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org