This all works fine, until you fire up a generator to charge batteries.  If the 
generator remains within voltage and frequency limits, you stand a good chance 
of overvoltaging the batteries.  In this situation it is best to disable the 
utility-interactive PV system while charging batteries from the generator.

The SMA system gets around this limitation by using RS485 communication between 
the SI and the SunnyBoys.  When set to off-grid mode, the Sunnyboys will limit 
their output power limit from 100% to 0% based on commands from the SI, so 
battery voltage can be limited, even when charging from the generator.


See ya!

Marv
Director of Technology and Support, North America
SolarEdge Technologies, Inc.
Tech Support North America:  +877.360.5292
Mobile: +530.392.0356

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian Faley
Sent: Friday, September 02, 2011 5:21 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling

Hi Allen,

I'll try to describe the typical AC coupled system as well as I can.

In such a system, a NON-grid tied battery based inverter (i.e. Magnum MS PAE) 
is connected as a backup inverter, only supplying AC power to consumer's loads 
when the grid is down. The micro inverter(s), or string inverters are connected 
on the load side of the inverters transfer switch, in parallel with the 
inverter output so they see AC grid power (when available) or inverter power 
when the grid goes down. The micro inverters / string inverters in such a 
system are called AC coupled inverters because the point of coupling is the AC 
system rather than the DC system. This allows the battery based inverter to 
provide the grid reference to the AC coupled grid-tied inverters when the 
utility power is not present - Backup mode. In that mode the inverter will form 
the reference for the grid tied inverters and any surplus power supplied by the 
grid-tied inverters that is not being consumed by AC loads will charge the 
battery of the inverter.  In this inverter mode, once the battery is full, the 
inverter senses it and shifts the inverter frequency by .5hz to force the grid 
tied inverters off, keeping them from exporting power, thereby stopping the 
battery from overcharging.

On a large system, a DC diversion load is usually added in parallel with the 
battery to reduce the on/off cycling of the grid tied inverters, which once the 
frequency shift happens, will try to reconnect every five minutes without it.
Using the frequency shift method only is rather crude, because it essentially 
is a bang/bang controller - off or on. Its not a matter of our lack of 
confidence in the approach, the question is do you want the battery voltage 
swinging around by several volts. In a DC diversion mode system, the surplus 
energy from the grid tied inverters can be put to work as a useful dump load 
rather than just off lining several kw of PV.

We had a white paper describing the AC couple mode. I'll see what we can do to 
make it more widely available, since the interest in such systems seems to be 
increasing.






Brian Faley

Chief Engineer

Magnum Energy

2111 W Casino Rd

Everett, WA 98204

425-353-8833

bfa...@magnumenergy.com<mailto:bfa...@magnumenergy.com>

________________________________
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Friday, September 02, 2011 4:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling

Brian,
Could you speak a bit more to this, please? My understanding is that the need 
with a string (or, I suppose, micro-) inverter and a battery-based inverter is 
for a way to disconnect full batteries from being overcharged when the grid is 
down and sell is disabled. The SMA approach is to shift frequency to reduce 
string inverter output. I thought that the battery-based (Outback, Magnum) 
approach is to use a contactor to open string inverter AC based on voltage 
(crude, but effective).

So what I understand is that the PAE inverters shift frequency: do you mean it 
simulates the shift that a Sunny Island would do? And if so, why is a diversion 
load recommended, and how is it configured into the system? And where can we 
read more about how this is designed to work?
Thank you,
Allan

Allan Sindelar
al...@positiveenergysolar.com<mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>

On 9/2/2011 4:39 PM, Brian Faley wrote:

Hi Larry,

Magnum MS PAE inverters do indeed shift the inverter output frequency

when the battery is full in order to disconnect grid-tied inverters used

in AC coupled systems. It was designed to work in conjunction with a DC

diversion load - which is recommended if the system is larger than a

couple panels.



Regards,



Brian Faley

Chief Engineer

Magnum Energy

2111 W Casino Rd

Everett, WA 98204

425-353-8833

bfa...@magnumenergy.com<mailto:bfa...@magnumenergy.com>




************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer 
viruses.
************************************************************************************
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to