Brian,

Is this the drawing?
Magnum ac coupled diagram from Google cache.

Kent Osterberg
Blue Mountain Solar



Allan Sindelar wrote:
Brian,
Good job of laying it out.

Now here's the part I'm missing. If as you say the grid-tied inverter(s), either micro or string, are connected to the load side of the inverter's transfer switch, then I presume that in "normal" (meaning grid is up) mode, the transfer switch is configured to allow the "protected load" (a.k.a. critical load panel or backed-up panel) to feed directly back to the main grid panel, in order to maintain selling to the utility. The Magnum is fed by another breaker in the main grid panel, in order to maintain battery charging. When the grid goes down, the transfer switch is manually switched to allow the grid-tied inverter(s) to directly feed the protected load panel, rather than the main grid panel. The output of the Magnum is capable of being backfed through the AC load output to function as a battery charger.

The Magnum has to be able to input on the AC load output in order to utilize the AC output of the grid-tied inverter(s). The grid-tied inverter(s) can't feed the main grid panel, as they would shut off during a grid outage. And the Magnum's AC input can't feed off of the protected loads panel, as its output also feeds that panel and it would then be trying to feed itself.

Am I even close here? It's enough to give an aging solar bozo a headache. I would appreciate a wiring diagram and clarification as to how such a system would be configured. And then there's the question of why it would even be done this way, using a battery-based inverter only for backup and a separate inverter(s) for grid-tie. What are the advantages to this approach over simply using a battery-based grid-interactive inverter, such as a GVFX, Radian or XW?

Thank you,
Allan
   
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com




On 9/2/2011 6:20 PM, Brian Faley wrote:

Hi Allen,

 

I’ll try to describe the typical AC coupled system as well as I can.

 

In such a system, a NON-grid tied battery based inverter (i.e. Magnum MS PAE) is connected as a backup inverter, only supplying AC power to consumer’s loads when the grid is down. The micro inverter(s), or string inverters are connected on the load side of the inverters transfer switch, in parallel with the inverter output so they see AC grid power (when available) or inverter power when the grid goes down. The micro inverters / string inverters in such a system are called AC coupled inverters because the point of coupling is the AC system rather than the DC system. This allows the battery based inverter to provide the grid reference to the AC coupled grid-tied inverters when the utility power is not present – Backup mode. In that mode the inverter will form the reference for the grid tied inverters and any surplus power supplied by the grid-tied inverters that is not being consumed by AC loads will charge the battery of the inverter.  In this inverter mode, once the battery is full, the inverter senses it and shifts the inverter frequency by .5hz to force the grid tied inverters off, keeping them from exporting power, thereby stopping the battery from overcharging.

 

On a large system, a DC diversion load is usually added in parallel with the battery to reduce the on/off cycling of the grid tied inverters, which once the frequency shift happens, will try to reconnect every five minutes without it.

Using the frequency shift method only is rather crude, because it essentially is a bang/bang controller – off or on. Its not a matter of our lack of confidence in the approach, the question is do you want the battery voltage swinging around by several volts. In a DC diversion mode system, the surplus energy from the grid tied inverters can be put to work as a useful dump load rather than just off lining several kw of PV.

 

We had a white paper describing the AC couple mode. I’ll see what we can do to make it more widely available, since the interest in such systems seems to be increasing.

 

 

 

 

 

Brian Faley

Chief Engineer

Magnum Energy

2111 W Casino Rd

Everett, WA 98204

425-353-8833

bfa...@magnumenergy.com

 


From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Friday, September 02, 2011 4:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling

 

Brian,
Could you speak a bit more to this, please? My understanding is that the need with a string (or, I suppose, micro-) inverter and a battery-based inverter is for a way to disconnect full batteries from being overcharged when the grid is down and sell is disabled. The SMA approach is to shift frequency to reduce string inverter output. I thought that the battery-based (Outback, Magnum) approach is to use a contactor to open string inverter AC based on voltage (crude, but effective).

So what I understand is that the PAE inverters shift frequency: do you mean it simulates the shift that a Sunny Island would do? And if so, why is a diversion load recommended, and how is it configured into the system? And where can we read more about how this is designed to work?
Thank you,
Allan
 

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


On 9/2/2011 4:39 PM, Brian Faley wrote:

Hi Larry, 
Magnum MS PAE inverters do indeed shift the inverter output frequency
when the battery is full in order to disconnect grid-tied inverters used
in AC coupled systems. It was designed to work in conjunction with a DC
diversion load - which is recommended if the system is larger than a
couple panels.
 
Regards,
 
Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
bfa...@magnumenergy.com


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to