Hi Drake,

A GENTRAN or equivalent is standard equipment for adding a backup generator to a house or small business as an alternative to one main manual or automatic transfer switch. It's simply a box with 8-12 individual transfer switch breakers some 120 and a few 240 - mostly 15 and 20 amp. They sell plug-in types and hard wire types where the output of a small gas generator is either plugged into the face of the unit or hardwired into the buss.

Then there is a bundle of wires that run from the GENTRAN to the house breaker panel. For each house circuit you want to backup you simply interupt the load line coming out of that main panel circuit breaker with the 2 lines from the individual transfer switches in the GENTRAN. So on the GENTRAN you switch each circuit between "GEN" or "Utility". Then you simply use the output of your new off-grid solar inverter to feed the GEN side and during a power outage you can not only switch your house over to your solar inverter with no dedicated critical loads subpanel but you can control how much load you want to put on your backup solar.

I've used 2 GENTRANS to cover all the circuits in a house - so IMHO it's better than a dedicated subpanel or an all-house automatic transfer switch in that you can pick and choose how much load you want to expose your inverter and batteries too. The only disadvantage is they only usually come in 15 and 20 amp circuits and usually offer only one or 2 240 Volt circuits. If you want to empower a 30 or 50 Amp 240 circuit - there are other companies that sell GENTRAN type switches with customizable breaker options but they are much more expensive.

Do watch your neutral and grounding circuits though. Since the neutral is bonded at the Main panel you want to be consistent with the "grounded conductor grounded at one and only one point rule" when the GENTRAN is installed and switched - a point many electricians miss when they install backup generators.

Hope that helps.

Jeff Clearwater
Village Power Design
NABCEP^(TM) Certified PV Installer
C-46 CA Solar Contractor


Drake wrote:
The GENTRAN sounds very interesting. The Internet has some for sale, but so far no detail. Will the 12 circuit panel shed one circuit at a time? In a nutshell, how does this work?


Thanks,

Drake



At 02:32 AM 11/10/2011, you wrote:
Hi Wrenchies,

Yes and if you use a GENTRAN or equivalent circuit-by-circuit transfer switch add-on for the output from the offgrid inverter to your AC panel - then there is no need for a separate dedicated AC loads panel and rewire like in Larry's original drawing. I've used this trick for years to avoid a dedicated subpanel for the output of an off-grid inverter. Combined with the DC transfer switch idea that high voltage MPPTs enable, (we've been waiting for this) you have a really simple retrofit for an on-grid system.

And now with Magnum and others offering low-power 120/240 split phase outputs in one inverter - the grid-tie hybrid retrofit market is getting more attractive all the time. DC Transfer Switch to MPPT Charger to 120/240 split phase inverter/battery to GENTRAN Switch. Getting cheaper all the time.

And hopefully one day not too far off SMA will bring their "Backup Set S" they show in their European catalog to the States- this is basically a 2.2 KW version of the Sunny Island - 2 of them would achieve 120/240 stacked and be a nice cheaper SB enabler as well.

Also your standard 100 AMP 4 pole DPDT transfer switch may not be rated for 600 VDC explicitly but think of it - the old knife style units "throw" is like 12" - no way that won't work with 600 VDC.

Hope that helps!,

Jeff





Larry Crutcher, Starlight Solar Power Systems wrote:

Right.... a major rewire and many components...and sacrifices. The
Outback is limited to 30 amps AC and cost much more than you would need
to spend.

With my idea you just add a transfer switch....Done. When the grid is
down, PV feeds HV CC. Then you can use ANY size inverter, with or without
a transfer switch. No rewiring the grid inverter. No 240 volt
transformers or dual inverters. No relays, switches or diversion
controllers. Batteries are always properly maintained. No phantom loads.
Very simple.

Thanks for your input. Now if I can just find that darn 600 volt transfer
switch.

Larry Crutcher
Starlight Solar Power Systems



On Nov 9, 2011, at 1:55 PM, Drake wrote:


Any amount of power will AC couple.
If you use an off grid inverter, such as an Outback, to feed the
protected load panel, the inverter should be fed by grid AC power to
supply loads, when the grid is available.  Just feed  your grid
tie inverter into the protected loads panel.   You will need a
relay to shut off power from the grid tie inverter when the batteries are
full.  This can be triggered by the fan relay in the Outback.

The on grid inverter will push power into the grid through the battery
inverter's internal transfer switch during normal operation and AC couple
when the power is out.  If your grid tie inverter is 240 volts, you
will need to use a transformer or two inverters.
The phantom load of the inverter can be eliminated by using a transfer
switch to send PV power straight to the grid, during normal grid
availability, keeping the inverter turned off.  AC coupling seems
much easier than using a charge controller, but there is no conditioning
of the batteries.  The charge is just on and off at the voltage set
point. For a back up system, that is not much of a problem, as the
battery inverter can maintain the batteries when power is available.



At 02:04 PM 11/9/2011, you wrote:

Nice Find, Drake! Thanks.

What is the minimum system for an AC coupled inverter?

Again, the idea is for low cost battery backup of an existing grid tie.
The AC coupled schematics I have looked at require a major rewire and
many components. I would like to hear if someone has a simple add on
solution compared to just switching the array to the high voltage CC.

Larry Crutcher
Starlight Solar Power Systems

_______________________________________________
List sponsored by Home Power magazine

List Address:

RE-wrenches@lists.re-wrenches.org  <mailto:RE-wrenches@lists.re-wrenches.org>

Options&  settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:

www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:

www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to