Hi
I have a system in operation since 2003 using 13 paralleled Outback MX 60 CC
and I have measured over 600 Amps at 48 Volts.on the common bus. Outback and I
replaced the fans in the MX 60s but we have had no failures. This power is
converted to 60 hZ using 12 Outback inverters, I have had an inverter trip off
on the DC side just the other day and I will check it out this comming week but
no problems.
DT
________________________________
From: "Larry Crutcher, Starlight Solar Power Systems" <la...@starlightsolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Friday, November 18, 2011 12:35 PM
Subject: Re: [RE-wrenches] High-power MPPT/Charge Controllers?
Sounds like a project for Sunny Island and the Boy's.
Larry Crutcher
Starlight Solar Power Systems
On Nov 18, 2011, at 10:49 AM, Exeltech wrote:
Need info on MPPT/charge controllers able to output up to 500A at 48Vdc.
>High-voltage DC input (up to 300Vdc) preferred. Units will connect to a
>20-24 kW PV array and 150 kW-h battery for a large off-grid system.
>Not locked into 48Vdc. Can go up to 108Vdc (nominal) if needed.
>
>Any such CC units available?
>
>If not, what's been the collective Wrench experience in paralleling multiple
>controllers of whatever max output amperage exists on the market? I realize
>a paralleled configuration of this nature would entail multiple separate arrays
>in use on the input. That won't be a problem. Just need to be able to feed
>the common battery bank.
>
>Thanks.
>
>Dan
>
> _______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>_______________________________________________List sponsored by Home Power
>magazineList Address: re-wrenc...@lists.re-wrenches.orgOptions &
>settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules
>& etiquette:www.re-wrenches.org/etiquette.htmCheck out participant
>bios:www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org