Larry,

I think Magnum's recommendation is more about proper battery charging than safety.

I'll second Kirpal's and Jeremy's recommendations for loads. The Tristar is probably the best choice for this job, but you are overestimating what you can do with it and paralleling two may have some coordination issues. The Tristar 60 manual says to keep diversion loads below 45 amps (or somewhere close to that). I think its a reliability issue so with a secondary shut down method, you might be okay pushing it a bit. I'm not sure how you get two of them to work together.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 11/29/2011 5:35 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
Hello Wrenches,

I would like some advice on diversion load control of 3800 watts of PV solar. 
The battery bank is 48 volts and the battery inverter is the MS4448PAE. This 
will AC couple with a grid tied inverter during an outage. Magnum Energy 
recommends the addition of a dump load for safe battery voltage control.  The 
customer may leave the home unattended for weeks so I am looking for 
reliability here. Quality, as well.

A pair of Tristar 60's should be suitable for the 3.8kW output but I haven't 
been able to find a load that is sized for this job. I welcome any advice on 
this subject.  Thanks in advance.

Larry Crutcher
Starlight Solar Power Systems
_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to