John,

Could you clarify units? "0.418 Liters/AH" is that per charge cycle? per hour? per minute? per cell?
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 1/5/2012 4:18 PM, John DeBoever wrote:

Hello Wrenches,

 

Here are some very general guidelines on the subject for consideration:

 

o   Free flow ventilation is required within lead acid battery room / enclosure:

Batteries produce Hydrogen during charge, depending on the specific design and application

The gassing appears approximately around 80%-90% SOC, depending on the specific design and application

The amount of gassing increase with the battery ageing

Hydrogen becomes explosive at a concentration of 4%

Hydrogen levels must be kept below 1% or 2% percent

Flooded batteries typically produce .418 Liters/AH of Hydrogen at STC, depending on the specific design and application

VRLA batteries typically produce .004 to .013 Liters/AH of Hydrogen at STC,  depending on the specific design and application

 

o   Cleaning maintenance guidelines:

Batteries are attract dust, dirt, and grime. Keeping them clean will help one spot trouble signs if they appear and avoid problems associated with grime.

1. Check that all vent caps are tightly in place.

2. Clean the battery top with a cloth or brush and a solution of baking soda and water. When cleaning, do not allow any cleaning solution, or other foreign matter to get inside the battery.

3. Rinse with water and dry with a clean cloth.

4. Clean battery terminals and the inside of cable clamps using a post and clamp cleaner. Clean terminals will have a bright metallic shine.

5. Reconnect the clamps to the terminals and thinly coat them with petroleum jelly (Vaseline) to prevent corrosion.

6. Keep the area around batteries clean and dry.

 

Hope this help,

 

John

 

John F. DeBoever

Global Projects & Technical Director – Renewable Energy

Trojan Battery Company

 

12380 Clark Street

Santa Fe Springs, CA 90670

Tel: +1-562-236-3000 Ext. 3139

Cell: +1-845-514-7600 – NY office time zone: USA EST (GMT-5)

Fax: +1-562-236-3239

jdeboe...@trojanbattery.com

www.trojanbattery.com

Description: Description: Description: Description:
              C:\Users\ecastro\AppData\Local\Microsoft\Windows\Temporary
              Internet Files\Content.IE5\0VK735AY\MC900116474[1].wmf

 

    Happy Holidays

 

 

 

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of bob ellison
Sent: Thursday, January 05, 2012 12:18 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] battery venting; Corrosion

 

I have had great luck by heating Vaseline to the hot liquid state then brush it on all the exposed lead and I dip the cable ends also.

Doing this I have had 1 terminal that got corroded out of several hundreds.

 

That gets you a thin coat and lasts for years.

"Clean and tight" is nice but it gets corroded at some point, and I hate cleaning 1 terminal or 20!

 

Later,

Bob Ellison

 

 

-----Original Message-----

From: re-wrenches-boun...@lists.re-wrenches.org

[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems

Sent: Thursday, January 05, 2012 10:37 AM

To: RE-wrenches

Subject: Re: [RE-wrenches] battery venting; Corrosion

 

Almost all RV's have a small, poorly vented battery box with 4 GC2 batteries. We see corrosion all the time. When we replace batteries, we use zinc coated copper terminals and apply a thin layer of grease with a toothbrush to every exposed portion of the connectors. This simple step, with the occasional reapplication, keeps all terminals as fresh as the day installed for many years. I am speaking from experience of hundreds of installations.

 

Larry Crutcher

Starlight Solar Power Systems

 

 

_______________________________________________

List sponsored by Home Power magazine

 

List Address: RE-wrenches@lists.re-wrenches.org

 

Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

 

Check out participant bios:

www.members.re-wrenches.org

 

 


This e-mail message and any attachments that accompany it may contain information that is confidential, privileged, or protected from disclosure. It is intended solely for the use of the individual(s) to whom it was intended to be addressed. If you have received this e-mail by mistake, or you are not the intended recipient, any reading, disclosure, copying or other use of this communication is strictly prohibited. If you have received this communication in error, please immediately advise the sender at their phone number listed above, or by electronic mail, and also permanently delete the original and all copies of this e-mail and any attachments from all locations. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to