Jeremy,

I would like to share few comments:

o   5 strings in parallel will definitely promote a high probability of 
unbalanced strings over time, leading to some units "boiling" while others will 
face sulfatation. 1 to 3 strings in parallel  max would be my recommendation, 
depending size of load application specifics and maintenance site specifics.  I 
would always personally try one to max 2 strings in parallel and there will be 
many reasons for that, too long to expand on for the purpose of this email. 
Please consider larger Ah battery units.

o   The charge rate of 3.3% of C20 battery capacity is very low, just able to 
face the self-discharge of the battery on a floating charge mode operation, not 
any of the site loads usage of the battery. You would need to clarify further 
when the 3.3% of C20 happen, if at finishing charge or during bulk charge.  I 
recommend you discuss directly with Trojan Tech Support for further help at 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top

o   The battery most likely were challenged by high sulfatation, resulting in 
loosing capacity  and generating heat. The units boiling would face corrosion 
aggression.

I hope this helps,

John
Trojan Battery Company

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of All Solar, Inc.
Sent: Tuesday, April 03, 2012 10:24 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charge Rate (Hot Trojan Batteries)

With 5 strings installed, I figured the charge rate to be about 3.3% (of C20 
rate) for 5 years or so. Actually since it was installed in 2002, and now on 
its second set of batteries.
We added some PV and an MX60 a year ago, and now this.  I think he had heavily 
sulfated batteries which eventually led to shorted cells. ?
Jeremy
----- Original Message -----
From: Jason Szumlanski<mailto:ja...@fafcosolar.com>
To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org>
Sent: Monday, April 02, 2012 1:43 PM
Subject: Re: [RE-wrenches] Hot Trojan Batteries

There are a lot of forums and circles where C/20 refers to the capacity divided 
by 20, or 5% of the battery capacity. This may be the more informal 
interpretation of the term, but you will find many examples where people 
consider C/20 to be 5% of the capacity (wrong or right). For example, look at 
the most frequently accessed deep cycle charging FAQ on the Internet: 
http://www.windsun.com/Batteries/Battery_FAQ.htm

To be clear perhaps we should just use plain English and say "the recommended 
charging rate is 10-15% of the capacity of the battery at the 20 hour discharge 
rate."

Jason Szumlanski
Fafco Solar


From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of Allan Sindelar
Sent: Monday, April 02, 2012 1:46 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Hot Trojan Batteries

Wrenches,
I attended John DeBoever's Friday afternoon presentation on battery technology 
and care at the NABCEP Continuing Education conference this past weekend. It 
quickly became clear to me that John seriously knows his batteries, at all 
levels: chemistry, physics, RE use and care, etc. It was an advanced-level 
presentation, and I learned a lot.

The first thing John told us was that English is not his native language; he's 
a Belgian raised in South Africa (and more that I didn't catch). He was 
bursting with knowledge and good information, but occasionally we in his class 
would back him up to better explain a point.

In short, I think he will be a real asset to the Wrenches list as a 
manufacturer's representative. And occasionally there will be something 
confusing, such as what just happened here. I too wondered about C20 versus 
C/20. I appreciate that he quickly cleared up the confusion, and look forward 
to learning quite a bit from his posts about battery issues.
Allan
Allan Sindelar
al...@positiveenergysolar.com<mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>



On 4/2/2012 11:00 AM, John DeBoever wrote:
Jason, Wrenches,

C/20 means C over 20 hours discharge rate = capacity @ the 20 hours discharge 
rate. C/20 often is mentioned as C20, so the confusion here.
Max recommended is 10& to 15% of C20 of the battery bank.

John
Trojan Battery Company

From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
Szumlanski
Sent: Monday, April 02, 2012 12:53 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Hot Trojan Batteries

There must be some confusion here about the charging rate. C/20 refers to 
capacity divided by 20, so in the case of a 325aH battery (capacity @ the 20 
hour discharge rate) we're talking about charging at a 16.25 amp rate. I'm sure 
John is not referring to a maximum rate of 10-15% of 16.25 amps, but 10-15% of 
the 325aH capacity.

Jason Szumlanski
Fafco Solar


From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of John DeBoever
Sent: Monday, April 02, 2012 12:14 PM
To: allso...@scswifi.net<mailto:allso...@scswifi.net>; RE-wrenches
Subject: Re: [RE-wrenches] Hot Trojan Batteries


Jeremy, Wrenches,



165°F is definitely too high and you should stop immediately any charge to 
avoid further major problems. I recommend you contact our Trojan Tech Support 
for help at 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top



Below are few perspectives to help the diagnostic:



o   System issues:

*  Check Charger setting: the C/20 rate mentioned is definitely too high and 
will damage the battery. The maximum recommended current rate is 10-15% of C/20 
for a deep-cycle flooded lead acid battery. Other C/rates are possible but are 
application specific and not typical.

*  Check Voltage settings: these are provided on Trojan datasheets, see here: 
http://www.trojanbatteryre.com/Tech_Support/literature.html

*  Check Temperature compensation: -0.028VPC for every 10°F above 77°F (add 
0.028 VPC for every 10°F below 77°F or subtract 0.020VPC for every 10°F above 
77°F. See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf

*  Check Voltage sensor status and connection. Dedicated wiring is recommended

*  Check temperature sensor. It shall be well positioned, typically in the 
middle of the battery bank at the warmest point.

*  Check if air circulation between the battery units.

*  Check if adequate air ventilation of the battery room.



o   Battery issues:

*  C/20 charging rate is too high (see above)

*  How old are the batteries? Ageing batteries will face micro-shorts that will 
decrease the battery turnaround efficiency over time that translates in higher 
temperature generation. Typically the battery temperature range is about 20oF 
above ambient temperature, and typical min and max limit are -4°F to 113°F.

See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf

165°F is way too high and will damage the units

*  Maybe you are facing one or more shorted units: check the voltage and it 
will quickly indicate if a unit is shorted.  Shorted units will generate heat 
and will jeopardize the charging of other units. Remove shorted units and 
consult tech support your charger supplier if possible to reconfigure of your 
battery bank with fewer units, configured at a lower battery bank voltage, 
using same voltage settings recommended by Trojan Battery Company.  Typically 1 
to 3 units less would be acceptable, depending the charger manufacturer 
settings.

*  Maybe you are facing sulfated batteries, resulting from low charging, thus 
resulting in lower overall turnaround efficiency. This will heat some healthier 
units of the battery bank, accelerating corrosion damages. The max temperature 
acceptable being 113°F, please consult Trojan Tech Support: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top

*  Please deal directly off-Wrenches list, with Trojan Tech Support for better 
fine tune resolution: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top



I hope this help,



John
John F. DeBoever
Global Technical Director - Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboe...@trojanbattery.com<mailto:jdeboe...@trojanbattery.com>
www.trojanbattery.com<http://www.trojanbattery.com/>



-----Original Message-----
From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
allso...@scswifi.net<mailto:allso...@scswifi.net>
Sent: Sunday, April 01, 2012 7:20 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Hot Trojan Batteries



Wrenches,

Can anyone explain why an L16 bank would be at 165F at rest.  Over a C20 charge 
rate, but I have a feeling there might be an internal short



Jeremy

All Solar

Sent via BlackBerry. Sorry for typos and shorthand!

_______________________________________________

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>





This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure. It 
is intended solely for the use of the individual(s) to whom it was intended to 
be addressed. If you have received this e-mail by mistake, or you are not the 
intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited. If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure. It 
is intended solely for the use of the individual(s) to whom it was intended to 
be addressed. If you have received this e-mail by mistake, or you are not the 
intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited. If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.





_______________________________________________

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>



________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to