Wrenches, In a job coming up I have a customer with an existing FM60 controller, 520 watt (!!) array. We are doing a ton of work, including adding a 4 kW solar array with Classic 150 charge controller. I am trying to figure out how to handle the GFP.
For the Classic, I need a 90 or 100 A output breaker minimum. 80 A is not an option. The OutBack dual GFP is 80 A, and so it not an option. Is there a 100 A GFP breaker assembly I have just never seen? Is there a way to use the Classic's GFP to run an external relay via AUX (to trip the FM60 output breaker at the same time)? Any ideas? Thanks, -Nathan -- Nathan J. Stumpff - Arctic Sun, LLC NABCEP Ceritified PV Installer #091209-175 nat...@arcticsun-llc.com<mailto:nat...@arcticsun-llc.com> Office: 907/457-1297
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org