Mark, Shorting the string should not be an issue. Unless you work at night, obviously there will be an arc when you cut the jumper, so remember to cover the whole string with an opaque covering beforehand I think I remember reading that somewhere?!?! Or just be careful, try to do it when the irradiance is low (less current), separate the cut wires quickly and make sure you have left enough wire in the box so that you are not working with short (and energized) wires in a metal box. put a wire nut on one wire while you handle and terminate the other.
A safer method, if possible, would be to leave an easily accessible module interconnection un-connected until you have terminated the home run (+)&(-), then go back and make the final module interconnection. Cheers, benn DayStar Renewable Energy Inc. www.daystarsolar.ca * Ph: 780-906-7807 Construction Electrician Solar Photovoltaic Systems Certified Certificate # 0007S HAVE A SUNNY DAY On 17/09/12 9:50 PM, "Mark Frye" <ma...@berkeleysolar.com> wrote: Wrenches, True or False: In a nominal sort of grid tied situation with string Voc at about 300 VDC and Isc at about 6 or 7 amps......It is OK to install modules on a roof in the sun and short the pos and neg together indefinitely. In other words modules can handle operating at Isc continuously without damage. It is only if you get localized shading AND a failed bypass diode that damaging hot spot heating can lead to failure? I am reviewing an installation manual that recommends completing the home run by connecting the pos and neg of the string with a single jumper cable, folding the cable on itself in order to push it through to a j-box and at some point later on, cutting the jumper in the j-box to terminate the pos and negs to the home run. I am concerned both about maintaining the string in a short circuit condition and cutting the jumper while energized. Any thoughts? Mark Frye Berkeley Solar Electric Systems
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org