Hi Brian,

Very good points. In function, the frames of the modules and the aluminum racking are grounding bus bars that are connected together with bolts and rivets (Weebs). This method is allowed by 250-64 C 2. All that is required is for inspectors / code writers to acknowledge that the frames and rails fit this definition. It may require additional wording or an exception.

This is not an issue of safety, function or science, but one of semantics.

Drake



At 05:31 PM 1/17/2013, you wrote:
Hi John,

You have brought up several points.

1. practical answer
The NEC says that a GEC can be solid aluminum. PV mounting rails are typically aluminum. It is easy to calculate the ampacity of a solid aluminum piece from its cross-section. Even the lightest rails on the market have an ampacity that is an order of magnitude greater than the copper wires required by code for GECs. The 2011 NEC, section 250.64(C)(3) says that "Bolted, riveted or welded connections of structural metal frames ... of structures" are permitted splices for the GEC. The WEEB is a tested and characterized device and therefore preferable to one that, while allowed by code, has not been characterized at all.

2. listing
There is no standard to list equipment for use as a GEC or an EGC. The lack of a standard does not mean equipment is not suitable, it just means we need to use good engineering judgement until the codes catch up. Does new equipment meet the intent of the existing code? Are there any valid engineering reasons not to use new equipment? I think those are the questions we should focus on. Note that the WEEB was introduced almost 7 years ago and these code issues still have not been resolved to everyone's satisfaction.

3. connecting to a copper wire
Jason Szumlanski discussed this already, but I will reiterate. When you connect a GEC to a string inverter it is done in a reversible manner, typical with a screw connection. When you connect to a PV system, consisting of multiple distributed inverters, you can do so with a reversible connection, typically a listed lug, anywhere on the PV system.

Best Regards,
Brian Wiley



On 1/17/2013 10:58 AM, John Berdner wrote:
Jay:

You raise an interesting question.

I believe the structure would have to be evaluated and Listed for equipment grounding (UL is working on a new Standard for this now) AND for use as a GEC (which I don't think is possible). Even if the WEEB was approved for use as a GEC (I still do not feel this is the case) the rail then needs to be contiguous or irreversibly spliced to the copper GEC.
I am not aware of any Listed hardware that facilitates this.
Anyone know of any ?

We also have a dissimilar metals problem irreversibly crimping or exothermic welding (the Code requirement) copper to aluminum.

Best Regards,

John Berdner
General Manager, North America



Solaredge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

From: <mailto:re-wrenches-boun...@lists.re-wrenches.org>re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, January 16, 2013 8:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

Dear John and Brian

Thanks for a great discussion.

My question is:

If you used a WEEB to connect the inverter to the rail, is the rack rail listed as a GEC?
Or does it have to be listed as a GEC?

Thanks

Jay

Peltz power





Sent from my iPad

On Jan 16, 2013, at 12:09 PM, Brian Wiley <<mailto:btwinfin...@gmail.com>btwinfin...@gmail.com> wrote:
Hi John,

I don't feel that you are argumentative. I am glad for this forum and people to put forth honest opinions.

I think you just may not be aware of how the WEEB actually works. It is a type of rivet, not just a pronged thing that makes connection as part of a bolted connection.

It does use a bolt to engage the part, but the teeth on the WEEB are specially shaped. When the bolt is torqued, the teeth deform, similarly to a rivet. The metal that it is connecting to mushrooms up around the tooth and the tooth pinches in around the metal. This deforming action is what forms an exceptional electrical connection and also forms an air-tight seal between the part and embedded metal to resist corrosion.

If you remove the bolt, the WEEB will still be connected to the metal. You must forcibly remove the WEEB from the metal.

Hope that clears things up for you.

Best Regards,
Brian Wiley





CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P  Please think of the environment before printing this email



_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Options & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to