Hi Dan,

The Iota jumper only raises voltage by 0.6 volts above the default setting. You 
will need to insert the jumper AND adjust the voltage POT (now internal) to 
reach the EQ range. 

For off grid systems, I usually turn up the Iota voltage POT fully since 
generator run time is rarely enough to cause a long over-voltage condition. 
Then when the customer wants to equalize, just continue running the generator. 
Sometimes I install a toggle switch in series with the jumper in case a lower 
voltage is desired.

Larry Crutcher
Starlight Solar Power Systems



On Jan 28, 2013, at 7:41 AM, Dan Fink wrote:

Carl;

The Iotas we are using have an external jumper that you insert that allows it 
to get to EQ voltage.

DAN