William,
Yes, that's my understanding. Outback acknowledged this to me
years ago.
Allan
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
On 1/29/2013 9:28 PM, William Miller wrote:
Allan:
Could it be that the SW systems are protecting the generator with
Generator Support, and the Outback inverters are not?
William Miller
At 07:18 PM 1/29/2013, you wrote:
This is going back
several
years...
The Outback VFX series lacks the tight input current regulation
of the SW
series, so the max AC amps in is really just a suggestion. In
many cases
(and especially with these small generators) we want to set the
max amps
in as high as possible to minimize charging time and maximize
C/rate. Yet
a surge load can momentarily exceed the max amps setting.
I have observed that the Honda inverter/generators have a quite
sensitive
AC output breaker, that will sometimes trip if a surge load
(such as a
refrigerator) comes on during a charge cycle set close to the
generator's
capacity. This incident was specific to a Honda 3000i. In
contrast,
Yamaha's EF3000iSE will lug when overloaded - not good for the
generator,
but also not likely to trip the output breaker.
This is a different issue than was being discussed, but fits
your
question.
Allan
|
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org