Hi Chris,

Thanks for a glimpse of how our German brethren handle PV design & installation. After all, who has more experience with design, execution, and funding than the Germans? There remains an arrogance that the US has a lock on how best to do any number of things. Hopefully, this antiquated attitude will change, soon; hopefully, before we are all reduced to asking the equivalent of, "Would you like to Supersize that meal?"

Best wishes on your install. Please keep us informed of how others around the world better handle these items.

Bill Loesch
Solar 1 - Saint Louis Solar

On 28-Mar-13 1:03 PM, Chris Mason wrote:
I am working on a large installation in a country that uses 230/400V 60Hz for the grid, so we had to look to Europe for the inverters and work 1000V. I spent some time on the phone with SMA Germany to discuss the reqiurements in Germany and to understand the design methodology the inverters were designed for. First of all, the inverters are gorgeous. The first one we installed is a 3Ph 17KW with 6 sets string inputs, 2 x MPPT. They connect the strings directly to the inverters, no disconnects. The inverters have a Electronic Solar Switch on the bottom, pull it down and the strings are disconnected. We are using 26 module strings or that install, which massively reduces cabling and components. I showed the engineer a photo of our larger installs, he laughed at the use of "pipes" for the cables. We install massive AC disconnects, they use a little isolator about the size of a Coke can.
Everything is a multi-core cable.

I also read a guide to the British Standards on PV installation, and their approach to grounding is absolutely different. Since PV conductors are all isolated now, they don't even want you to ground the array structures, in fact they describe grounding as a shock hazard. Very different mentality. I might think that the US way is likely safer if we were comparing with China or the third world, but this is Germany. I think they know electricity.

Chris


On Wed, Mar 27, 2013 at 12:16 PM, John Berdner <john.berd...@solaredge.com <mailto:john.berd...@solaredge.com>> wrote:

    Exposed single conductor sunlight resistant cable in cable trays
    are widely used in PV systems outside the US.

    There is a very large installed base of systems with good long
    term performance data using this type of construction.

    We should not discount the advantages of wire cable trays just
    because we are unfamiliar with it.

    Look at data cabling – Characterized by many, relatively small,
    cables over long distances with periodic drops.

    Sounds a lot like PV source circuits (other than voltage and
    current in the wires of course).

    There are lots of videos out there showing how to pull 10’s of
    pairs of wires simultaneously in cable trays.

    IMHO, we need to look at ideas like this to reduce installation
    cost and time.

    Installation costs are becoming the tall pole in the tent and new
    thinking is needed.

    As systems are falling to sub $3.00 /Watt all-in, running wire in
    conduit will simply not be cost effective.

    Running wire in conduit is one of the reasons PV installation
    costs in the US are double (or more) of those in Europe.

    As one of my former German colleagues noted:

    “It is only in the US where you need first to be a plumber before
    you can be an electrician”

    Best Regards,

    John Berdner

    General Manager, North America

    SolarEdge Technologies, Inc.

    3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of
    our new address.)/*
    T: 510.498.3200, X 747 <tel:510.498.3200%2C%20X%20747>

    M: 530.277.4894 <tel:530.277.4894>

    *From:*re-wrenches-boun...@lists.re-wrenches.org
    <mailto:re-wrenches-boun...@lists.re-wrenches.org>
    [mailto:re-wrenches-boun...@lists.re-wrenches.org
    <mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of
    *Allan Sindelar
    *Sent:* Wednesday, March 27, 2013 8:51 AM


    *To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] Cable tray

    Andrew,
    We have used #10 USE-2 for about 16 years, and our high-elevation
    New Mexico sun is quite intense. I have yet to see any degradation
    exceeding fading discoloration on any conductors from that far
    back, even when directly exposed to sunlight. No cracking,
    peeling, delaminating, or hardening.
    Allan

    *Allan Sindelar*
    al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
    NABCEP Certified Photovoltaic Installer
    NABCEP Certified Technical Sales Professional
    New Mexico EE98J Journeyman Electrician
    Founder and Chief Technology Officer
    *Positive Energy, Inc.*
    3209 Richards Lane (note new address)
    Santa Fe, New Mexico 87507
    *505 424-1112 <tel:505%20424-1112>*
    www.positiveenergysolar.com <http://www.positiveenergysolar.com/>

    On 3/27/2013 8:41 AM, Andrew Truitt wrote:

        Bill - What is your take in conductor insulation degradation
        over time when exposed to UV? Regardless of the "sunlight
        resistant" labeling, USE-2 (and I assume PV wire though I
        haven't seen it yet) does show wear after years of exposure to
        direct sunlight.  Maybe best practice would be to use cable
        trays where conductors are shaded and [properly installed]
        conduit when exposed to direct UV?

        - Andrew Truitt



        Sent from my iPad


        On Mar 26, 2013, at 11:55 PM, "Bill Brooks"
        <billbroo...@yahoo.com <mailto:billbroo...@yahoo.com>> wrote:

            William,

            I have all the respect in the world for you, but I’m not
            referring to “basket tray”, which is only appropriate for
            small conductors. I’m talking about legitimate cable tray
            that can be up to 12” wide and that has a top and rungs
            every 12”. The main facilities that use it in the United
            States are large industrial facilities. Most electricians
            don’t get to work with it. It is clearly superior to EMT
            and is at least as good as IMC without all the hassle of
            threaded fittings and setting up expansion joints and
            worrying about 20 years of conductors thermal cycling.
            Even the best electricians have problems with this stuff.

            I am talking about projects with 800 foot long feeder
            runs. We can bring them in the building and build a rack
            for the conduit or run covered tray outside. As the 2014
            NEC will require, you will have to use contactor combiners
            or some other means to shut down the conductors inside a
            building. It’s all doable. My recommendation after seeing
            the aftermath of rooftop conduit by good electricians is
            to put cable tray on roofs and use conduit if you bring
            the feeders indoors. It will become common practice soon.
            Hopefully sooner than later.

            Bill.

            *From:*re-wrenches-boun...@lists.re-wrenches.org
            <mailto:re-wrenches-boun...@lists.re-wrenches.org>
            [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
            Behalf Of *William Miller
            *Sent:* Tuesday, March 26, 2013 9:49 PM
            *To:* RE-wrenches
            *Subject:* Re: [RE-wrenches] Cable tray

            Bill:

            I have to disagree with you on this one.  We can not
            abandoned a tried and true practice just because some
            practitioners don't do it right.  I don't know how one can
            justify saying that encapsulating high voltage conductors
            in a conduit is less safe than exposed in a flimsy
            basket.  Consider snow and ice and falling objects.

            Too many installers entered the PV field without first
            acquiring the necessary skills as journeymen or women
            electricians.  I don't see the benefit of rewriting the
            code to accommodate a lack of skills in the industry.

            Respectfully,

            William Miller

            PS:  The temperature adders always encourage us to enter
            the building envelope at the first appropriate location to
            avoid adding them.  Thoughtful installers will do the same.

            Wm


            At 10:15 PM 3/25/2013, you wrote:


            Content-Type: multipart/alternative;
                    boundary="----=_NextPart_000_00E3_01CE29A6.37CC5110"
            Content-Language: en-us

            William,

            I would strongly disagree that conduit is tried and true
            on rooftops. I have rarely seen good conduit runs on
            rooftops. Most electricians have no clue how to work with
            expansion joints. Conduit on rooftops is a bad idea in
            general. Most conduit runs in big buildings are all done
            indoors for good reason. We are the crazy people doing
            things on the roof.

            The sooner we get away from conduit­particularly for long
            feeder runs­the better.

            In Europe they don’t have problems with their rooftop
            wiring systems because everything is in tray.

            For those that don’t allow cable tray for anything less
            than 1/0, just remember that if it isn’t called cable
            tray, then 392 doesn’t apply. The NEC would allow us to
            use treated lumber in place of cable tray. This makes no
            sense.

            We did some research on the origin of the 1/0 requirement,
            and it is ancient and no longer relevant. Just because it
            is in the code, does not mean it is correct. That’s why we
            try to fix it every three years.

            Bill.

            _______________________________________________
            List sponsored by Home Power magazine

            List Address: RE-wrenches@lists.re-wrenches.org
            <mailto:RE-wrenches@lists.re-wrenches.org>

            Change email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>




        _______________________________________________

        List sponsored by Home Power magazine

        List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

        Change email address & settings:

        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:

        www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

        Check out participant bios:

        www.members.re-wrenches.org  <http://www.members.re-wrenches.org>

    CONFIDENTIALITY NOTICE: This e-mail and its attachments are
    intended only for the use of the individual or entity who is the
    intended recipient and may contain information that is privileged,
    confidential and exempt from disclosure or any type of use under
    applicable law. If the reader of this e-mail is not the intended
    recipient, or the employee, agent, or representative responsible
    for delivering the e-mail to the intended recipient, you are
    hereby notified that any dissemination, distribution, copying, or
    other use of this e-mail is strictly prohibited. If you have
    received this e-mail in error, please reply immediately to the
    sender.

    *P*  Please think of the environment before printing this email


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com <http://www.cometenergysystems.com>
Cell: 264.235.5670
Skype: netconcepts


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com <http://www.avg.com>
Version: 2013.0.2904 / Virus Database: 2641/6206 - Release Date: 03/26/13





-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2904 / Virus Database: 2641/6206 - Release Date: 03/26/13
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to