Belated thanks for the replies on this, Jason et al. Sorry for my lack of a clear explanation- Jason interpreted me correctly. Apparently this Lennox unit was installed without a neutral- I'm awaiting more info from the PE.

On 2013/7/5 19:25, Jason Szumlanski wrote:

I think what Dave is saying is that the enphase cable neutral is connected to the EGC in the roof mounted j-box, and no neutral is run to the Lennox panel or disconnect. While the neutral should not carry line current under normal operation, Enphase calls it a neutral - look up the NEC definition of neutral. I can see an AHJ having reservations about this, whether the "combined Neutral/EGC/GEC" is bare or insulated.

I would not waste time trying to argue this with the AHJ. I would bring three current carrying conductors plus a combined EGC/GEC to the main distribution panel, just like every other Enphase job we do.

I spend a fair amount of time explaining how this solar powered air conditioner is nothing revolutionary, except for the creative marketing. Anyone out there try to team up with a HVAC company to market any A/C unit as solar powered?

Jason Szumlanski
Fafco Solar

On Jul 5, 2013 5:14 PM, "August Goers" <aug...@luminalt.com <mailto:aug...@luminalt.com>> wrote:

    Hi Dave,

    I'm not sure I'm understanding your scenario clearly but I'll take
    a crack
    at it. The Enphase system should have a bare #6 GEC for each micro
    and can
    then transition to a #8 green GEC once in conduit and run all the
    way back
    to the main ground electrode system. The #6 and #8 should be
    irreversibly
    crimped together since the GEC needs to be continuous. Certainly
    it is not
    okay for the neutral in the Lennox panel to be bare unless it is
    somehow a
    main panel. You could run the DC GEC along with the other
    conductors and
    it can serve as a dual purpose GEC and equipment grounding
    conductor per
    2011 NEC 690.47(C)(3).

    Best,

    August
    -----Original Message-----
    From: re-wrenches-boun...@lists.re-wrenches.org
    <mailto:re-wrenches-boun...@lists.re-wrenches.org>
    [mailto:re-wrenches-boun...@lists.re-wrenches.org
    <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of
    Dave Click
    Sent: Wednesday, July 03, 2013 6:26 AM
    To: RE-wrenches
    Subject: [RE-wrenches] EGC for Enphases

    All,

    I was just looking at small 4-module Andalay (Enphase 190) system
    tying
    into one of the Lennox solar-ready air conditioners. The engineer had
    specified the 690.47(C) GEC be run directly from the array down to the
    existing electrode. Running from the inverters is a 2+G wire to
    the Lennox
    panel; they are using the uninsulated ground as the circuit
    neutral. It
    seems to me that this violates 200.7 (grounded conductor marked
    white or
    grey). Also, 250.134(B) (EGC run with circuit conductors), about
    which the
    engineer states "I have been studying the NEC on this and I
    believe that
    the intent is to permit the ground to be carried with the current
    carrying
    conductors, not require."

    Am I missing something?

    Thanks,
    Dave
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to