All,

I was just looking at small 4-module Andalay (Enphase 190) system tying into one of the Lennox solar-ready air conditioners. The engineer had specified the 690.47(C) GEC be run directly from the array down to the existing electrode. Running from the inverters is a 2+G wire to the Lennox panel; they are using the uninsulated ground as the circuit neutral. It seems to me that this violates 200.7 (grounded conductor marked white or grey). Also, 250.134(B) (EGC run with circuit conductors), about which the engineer states "I have been studying the NEC on this and I believe that the intent is to permit the ground to be carried with the current carrying conductors, not require."

Am I missing something?