Hi Eric, Sounded like bad batteries to me also (I think he called in this AM). He has (2) XW6048 units that are capable of 200ADC between them, and he also has 1260Ah of flooded capacity. DC Start V is set for 46.5V, so if we assume he was close to 50%
discharge (depending on load), it should take almost 2 hours to reach the bulk voltage (80% replaced). His batteries were ramping up to bulk in just a couple of minutes, meaning the batteries were not absorbing the charge. I have heard varying opinions on the symptoms of sulfation, but it does sound like a battery issue (5 yrs old). He was advised to equalize to try and recover them (he has never done this), or replace them. Rgds, _____________________________________________________________________________________ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com/solar | Address: 250 South Vasco Rd., Livermore, CA 94551 *** Please consider the environment before printing this e-mail From: "SunHarvest" <e...@harvesthesun.com> To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Date: 08/07/2013 12:39 PM Subject: [RE-wrenches] SW AGS Sent by: re-wrenches-boun...@lists.re-wrenches.org I read through the archives on the XW AGS thread but have a query on behalf of a customer with an SW AGS issue. I'm heading out to the remote site tomorrow and would like, if possible, to show up knowing what I might be up against. The customer recently replaced his AGS for his two SW 6048s and then upgraded his firmware a week later. He reported that his problem with the AGS began after firmware upgrade. Here's the particular issue: AGS will try to start the 15.8kW Multi-Quip genny due to low battery voltage (event 306 DCV start). After about 5 minutes the AGS will stop the genny due to battery absorption level reached (event 313 ABS stop). The AGS will go through this event 306/313 cycle on and off until the homeowner shuts down the AGS. To me this sounds like bad batteries. But, the homeowner says this cycling does not occur when he manually starts the generator. This doesn't sound like a complicated problem but so far I'm unfamiliar with the SW AGS. So, I would greatly appreciate any insight you guys can offer me. Thanks!! Eric SunHarvest 001.530.798.3738 (Cell) ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. ______________________________________________________________________ _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
<<image/jpeg>>
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org