Sounds like you talked to the right guy, that's his info...except that he has, 
according to what he told me, an SW not an XW. I'm assuming he's maybe at 50% 
capacity on his original 1260Ah bank based on everything he told me this 
morning. He did say that his bank will last him through the night and that he 
has some pretty hefty air conditioning loads. He also said he had equalized in 
the past but not in the last 18 months. I'm just not convinced that his 
batteries are shot. But all this battery talk may be beside the point if he's 
not experiencing the same on/off cycling problem when he manually starts the 
genny, right? That is, assuming the disco settings remain in effect regardless 
of start mechanism. Thanks for indulging me tocayo.

Eric
SunHarvest
001.530.798.3738 (Cell)

  ----- Original Message ----- 
  From: eric.bent...@schneider-electric.com 
  To: RE-wrenches 
  Sent: Wednesday, August 07, 2013 12:54 PM
  Subject: Re: [RE-wrenches] SW AGS



  Hi Eric, 
   Sounded like bad batteries to me also (I think he called in this AM). He has 
(2) XW6048 units that are 
  capable of 200ADC between them, and he also has 1260Ah of flooded capacity. 
DC Start V is set for 46.5V, so if we assume he was close to 50% 
  discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
  in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
  but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace them. 
  Rgds, 

  
_____________________________________________________________________________________
 

  Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
|   Technical Support Representative 
  Phone: +(650) 351-8237 ext. 001#  |   
  Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., Livermore, 
CA 94551 


  *** Please consider the environment before printing this e-mail 



        From:  "SunHarvest" <e...@harvesthesun.com>  
        To:  "RE-wrenches" <re-wrenches@lists.re-wrenches.org>  
        Date:  08/07/2013 12:39 PM  
        Subject:  [RE-wrenches] SW AGS  
        Sent by:  re-wrenches-boun...@lists.re-wrenches.org 


------------------------------------------------------------------------------



  I read through the archives on the XW AGS thread but have a query on behalf 
of a customer with an SW AGS issue. I'm heading out to the remote site tomorrow 
and would like, if possible, to show up knowing what I might be up against. 
    
  The customer recently replaced his AGS for his two SW 6048s and then upgraded 
his firmware a week later. He reported that his problem with the AGS began 
after firmware upgrade. Here's the particular issue: 
    
  AGS will try to start the 15.8kW Multi-Quip genny due to low battery voltage 
(event 306 DCV start). After about 5 minutes the AGS will stop the genny due to 
battery absorption level reached (event 313 ABS stop). The AGS will go through 
this event 306/313 cycle on and off until the homeowner shuts down the AGS. To 
me this sounds like bad batteries. But, the homeowner says this cycling does 
not occur when he manually starts the generator. This doesn't sound like a 
complicated problem but so far I'm unfamiliar with the SW AGS. So, I would 
greatly appreciate any insight you guys can offer me. 
    
  Thanks!! 
    
  Eric
  SunHarvest
  001.530.798.3738 (Cell) 

  ______________________________________________________________________
  This email has been scanned by the Symantec Email Security.cloud service.
  
_____________________________________________________________________________________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org






------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

<<image/jpeg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to