I believe this is the tenK solar product being talked about. 

Jay
Peltz power

Sent from my iPhone

On Sep 18, 2013, at 8:49 AM, August Goers <aug...@luminalt.com> wrote:

> Hi Charlie,
>  
> I can't help but be intrigued by your setup here. It seems like the complete 
> opposite of where our commercial systems are going with transformerless 1000 
> V inverters entering the market. Anyway, I'm sure it's an interesting project 
> and there may very well be advantages to the system you're building.
>  
> I agree with Dave below that you should be okay with a #6 run to a ground 
> rod. Otherwise, your logic for sizing the GEC seems correct. We deal with 
> this similar issue when designing battery backup systems and the GEC can get 
> unwieldy very quickly. I would just point out your sizing logic per 
> 250.166(C) on your plans for the inspector to see.
>  
> Best,
>  
> August
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
> Sent: Wednesday, September 18, 2013 5:38 AM
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system 
> with microinverters
>  
> I think Gary may be overthinking this. If the micro-inverters have a GEC lug 
> then you'll need to run a GEC.
> 
> If you run your GEC to a ground rod, then you don't need to use one larger 
> than #6 per 250.166(C). (note also (D) and (E) but they're less useful to you 
> here)
> 
> Commentary:
> It makes no sense to me why the NEC can require a 0.9in diameter, #600mcm GEC 
> for some systems (not this one) per 250.166(B) and then say "oh wait, you 
> installed a single ground rod? Then a #6 is all you need!" in 250.166(C). But 
> it certainly makes our lives easier.
> 
> If the building GE is not a ground rod, you could still run your #6 GEC to 
> that new ground rod, and then bond that rod to the existing electrode using 
> whatever size jumper is required per 250.53 (which I believe would also be a 
> #6). This lets you keep that 300' run as a #6 rather than a #4 or #2 that may 
> be required otherwise.
> 
> DKC
> 
> On 2013/9/17 23:56, Gary Willett wrote:
> Charlie:
> 
> The answer depends on whether the "system" (modules and micro-inverters) is 
> "grounded" or "ungrounded". I think you are describing a "grounded" system, 
> but it's not totally clear based on your issue description.
> 
> If the micro-inverter is "transformer-less" the conductors are not isolated 
> between the DC-in and the AC-out. This requires the micro-inverter to have no 
> DC-side system ground. The micro-inverter AC-side always requires an EGC.
> 
> I am assuming that the PV modules are in close proximity to the 
> micro-inverters, and the 300' home-run is for the AC outputs of the 
> micro-inverters.
> 
> Is either DC bus (PV+ or PV-) a grounded conductor, or are both busses 
> ungrounded? If the DC-side combiners and re-combiners have OCPDs and 
> disconnecting means for both PV+ and PV-, then your system is considered to 
> be "floating" or "ungrounded".
> 
> If the system is "ungrounded", a GEC is not required on the DC-side of the 
> micro-inverter, and only an AC-EGC sized per NEC 690.45 is required.
> 
> If the DC-side combiners and re-combiners have OCPDs and disconnecting means 
> for only one conductor (PV+ or PV-), then your PV system is considered to be 
> "grounded". If the system is "grounded", the combined DC-GEC and AC-EGC 
> sizing requirements in NEC 690.47(C)(3) apply. The larger of the EGC (Table 
> 250.122) and GEC [250.166(B)] sizes will be required.
> 
> More specifics on the PV module Vmpp and micro-inverter you're dealing with 
> would be helpful.
> 
> Regards,
> 
> Gary Willett
> Icarus Solar
> 
> 
> On 9/17/13 8:37 PM, Aladdin Solar wrote:
> We will be installing a 40KW grid-tied PV system that uses PV modules wired 
> in parallel as per the module manufacturer -- so it's a high amperage, low 
> voltage system on the DC side. 2 branches of about 3KW of parallel wired 
> modules each come together onto a DC bus. The DC branch conductors are sized 
> as 2AWG.
>  
> The inverter system provided by the manufacturer consists of a number of 
> UL1741 single phase microinverters that all are powered off of the low 
> voltage DC bus. So there's a bunch of microinverters in parallel, combined 
> output is single phase power.
>  
> Those microinverters have a ground lug labeled "GEC". You know where this is 
> going...
>  
> Assuming we are following NEC 690.47(C)(3), we'll be treating this ground as 
> GEC and following all the GEC rules. My understanding is that because the DC 
> conductors within the array are 2AWG (NEC 250.166(B), we will need to connect 
> all 12 branches and 6 DC buses with continuous 2AWG and bring it all the way 
> back 300' to where the AC GEC bond is located. We're getting a lot of 
> pushback from the electrical sub and even some disagreement from the module 
> manufacturer on this--no one's ever seen a grounding conductor of this size 
> being required for this application.
>  
> Please don't get too bogged down with understanding the low voltage, parallel 
> module spec and the massive number of microinverters involved. What I'm 
> looking for is confirmation that I am properly understanding how the NEC GEC 
> requirements apply, especially to the GEC size.
>  
> Charlie Pickard
> NABCEP Certified PV Installation Professional ™
> Aladdin Solar, LLC
> 
> 
> __________ Information from ESET NOD32 Antivirus, version of virus signature 
> database 8813 (20130917) __________
> 
> The message was checked by ESET NOD32 Antivirus.
> 
> http://www.eset.com
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
>  
> List Address: RE-wrenches@lists.re-wrenches.org
>  
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>  
> Check out participant bios:
> www.members.re-wrenches.org
>  
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
>  
> List Address: RE-wrenches@lists.re-wrenches.org
>  
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>  
> Check out participant bios:
> www.members.re-wrenches.org
>  
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to