Yes, Jay, this is a TenKSolar system -- they certainly do have a habit of 
taking the 'thinking outside the box' approach!

The microinverter manufacturer states in their installation manual, "Connect 
the grounding electrode conductor to the microinverter ground clamp" so it's 
quite clear we are dealing with GEC rules.

Thanks for all your comments and the reminder of the NEC 250.166(C) exception 
which I hadn't really connected with before. 

I'm having difficulty understanding what the requirement in that paragraph 
actually means. When it states "that portion of the grounding electrode 
conductor that is the sole connection to the grounding electrode shall not be 
required to be larger than 6AWG..." -- what does "that portion" and "sole 
connection" mean? If we have a number of GEC branches from that are 
irreversably spliced to a single 6AWG conductor bonded to the grounding 
electrode, do those various GECs affect the "that portion" and "sole 
connection" at all?

Charlie Pickard
NABCEP Certified PV Installation Professional T
Aladdin Solar, LLC
 

  ----- Original Message ----- 
  From: Bill Brooks 
  To: 'RE-wrenches' 
  Sent: Wednesday, September 18, 2013 2:42 PM
  Subject: Re: [RE-wrenches] GEC sizing for a high amp,low voltage PV system 
with microinverters


  Nick,

   

  Thanks for the clarification-it is a mysterious threaded hole..

   

  Bill.

   

  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
  Sent: Wednesday, September 18, 2013 10:19 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system 
with microinverters

   

  Hi Bill and wrenches,

  To clarify, our new Enphase M250 microinverter does not have a grounding 
terminal.  The grounding of the M250 will be provided through the Engage cable. 
 We only have a hole in the lid, in the rare case that a lug will be desired or 
required by the AHJ, but we do not provide the grounding clip with the 
microinverter.  A grounding terminal can be added to the microinverter.  We 
have an application note on alternate grounding methods for the M250, if needed.

   

 

  __________ Information from ESET NOD32 Antivirus, version of virus signature 
database 8815 (20130918) __________

  The message was checked by ESET NOD32 Antivirus.

  http://www.eset.com



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org




  __________ Information from ESET NOD32 Antivirus, version of virus signature 
database 8815 (20130918) __________

  The message was checked by ESET NOD32 Antivirus.

  http://www.eset.com




__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 8817 (20130918) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to