Larry:

Maybe a better approach might be to use an inverter with "Gen-support."
That is unless a system already exists that does not have this feature.

Plan B:  use the gen start signal to disable one or more of the larger
loads.

I know this is not what you asked for, just trying inject some different
ideas.

William
-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar Power Systems
Sent: Monday, September 30, 2013 1:02 PM
To: RE-wrenches
Subject: [RE-wrenches] Generator automatic disconnect

Wrenches,

I want to use the Ecogen 6kW generator on a large off grid system. The
location has very few overcast or rainy days and the generator will rarely
be needed. My concerns is nuisance tripping the generator output breakers if
the household load exceeds 6kW. The power system control has a feature for
reducing the AC current used to charge the batteries but does not have a
feature for disconnecting the AC input based on input load.

Does anyone have a solution for monitoring AC load from the generator and
disconnect it if overloaded? It must automatically reconnect after a short
timeout.

Thank you,
Larry Crutcher
_____________

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to