Larry, one other consideration:
My own Ecogen appears to be able to produce well over its rating. I have never had an amp-clamp with me when I have observed this, but it appears to be quite able to do so. My Magnum 4024 will charge at 114A (as measured on a TriMetric 2025) at 28V DC, or 3,200 watts after efficiency losses, while at the same time passing through both microwave and toaster, which are both being run directly off of the gennie as pass-through loads, as the TM's amps in doesn't diminish significantly. Note that this is at 6,700' elevation, which would suggest about a 23% derating, or about 4,600 watts available. I'm sorry to not be more precise - I really should test it. But the point is that you may have more headroom than you think. My output breaker is 50A 1P, so I assume the 240V option would be 25A 2P. You might consider increasing this to 30A if your concern is nuisance tripping. Also, the QO breakers have a trip curve to allow minor surges. Allan Allan Sindelar A
Certified B CorporationTM
3rd option would be to have a separate charger (IOTA) that just runs from the generator. No pass through loads to the generator. |
_______________________________________________ List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org