Eric,
A Trace 2548 with automatic generator start? I don't believe there ever was such a thing. I suspect that you're referring to either a SW4048 or SW5548. If so, your first step is to check the error codes, some of which are found in Menu Heading 2 (for generator-related issues) and the rest in Heading 5. Any "Yes" message as you scroll through them is a good hint.

This inverter is at least 13 years in service, likely more. Sounds like a pre-GTI Y2K system. The units are remarkably robust and reliable, but it may well have a glitch in the firmware or voltage/frequency sensors. The extra inverter is your ace in the hole, once you determine what the issue is.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507

505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

 

On 10/17/2013 10:41 AM, SunHarvest wrote:
I have encountered a Trace 2548 in seemingly good working condition. I was called out to troubleshoot a Grid-tied, battery back-up system with the following problem:
 
- Upon loss of grid power there is about a 5 second lapse (no power to house) before the BB system engages. Power to the critical loads panel from the Trace is restored after the 5 second lapse.
- After another 5 seconds the Trace will disconnect power to the loads. This on-off cycle continues until grid power is restored.
 
After checking voltage & S.G. values, I determined that the 11 year old batteries needed to be replaced and I assumed this was the cause of the Trace on-off cycling.
I also found that half of his PV array had bad BP modules. BP replaced all of the modules under somewhat of a warranty. So, new modules, new batteries, and a new Outback FM60 charge controller. After all upgrades I ran through a simulated power outage again and the intermittent power problem persists!
 
He also has gen support enabled - connection to an Onan "RV Genset BGE NHE (??) - and when I start the genny from the inverter, by selecting "On" not "Auto", the genset fires right up but only stays on for about 30 seconds before it too shuts off and enters a cycling between auto-starting from the inverter and shutting down.
 
This behavior is beyond me. So, I'm seeking help from the pros. Anyone know what's going on here? The customer has another Trace 2548, unused, sitting in a box. So, if I needed to I could swap out the inverter and see if that makes a difference...?
 
Eric
SunHarvest
(530)798-3738


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to