Dan,
I think this thread applied not to OCDs but to an unfused 600VDC disconnect can 
mounted on a roof which is less than vertical.
Bob-O
On Nov 11, 2013, at 9:21 AM, Exeltech wrote:

Wrenches,

There appears to be some misinformation getting into this thread.

The "trip" mechanism within standard thermal over-current protective devices 
("OCP devices") is mechanically spring-loaded, and is triggered by heat.

Eric mentions below that Square D breakers are tested in a vertical orientation 
only - the implication being that's their only "UL certified" position.  If 
this were true, it would imply the breakers cannot be used in any other 
orientation.  This would potentially limit the Square D OCP market to 
sub-panels and other enclosures where the devices are vertical.  Inasmuch as 
the vast majority of panelboards I've encountered in my 40+ years in this 
industry have the breakers stacked horizontally, it would not be a wise 
business decision for the manufacturer to self-inflict such a limitation on 
their product.

This also does not mean any such limitation (real or not) applies to all 
breakers.

By way of example, OCP devices work in a horizontal position, stacked "pancake" 
style in a main panelboard, as well as vertically oriented side-by-side in a 
sub-panel.  In either orientation, they are  in full compliance with UL 489, 
(UL Standard for Circuit Breakers, Switches, and Circuit Breaker Enclosures).  
If an OCP device *was* positionally-sensitive, UL Standards require this 
sensitivity to be noted in the documentation accompanying the device.  Further 
to that point, UL 489 Section 7.1.1.13 states: "In determining if a circuit 
breaker complies with the test requirements, the device shall be mounted or 
supported as in service and tested under conditions approximating those of 
intended operation, except as otherwise noted."

Mounting position notwithstanding, a greater concern would be the ambient 
temperature of a rooftop location, whereby summer heat would tend to make the 
OCP device more sensitive than necessary, potentially causing it to trip at an 
amperage below that of its UL ratings.  While a nuisance, a more serious issue 
arises when operating the OCP device in cold ambient conditions, whereby the 
device may allow MORE than its rated trip current to flow.

Per UL 489, OCP devices are tested at either 25C or 40C ambient.  Again per UL 
489, if an OCP device is to be used in ambient conditions other than those two 
ranges, the acceptable temperature range for that OCP device shall be marked on 
the body of the device.

In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3, mechanical 
vibration testing is conducted with OCP devices oriented vertically, 
horizontally, and inclined 30 degrees from vertical, with all devices energized 
up to 200% of the device rated current during the testing.

Given the preceding, and per implication of UL 489 testing methods, OCP devices 
are NOT positionally sensitive.

In conclusion, if you DO install a rooftop OCP system, and for proper 
protection, please ensure the OCP devices utilized are rated for the worst-case 
ambient temperatures involved.


Regards to all,


Dan Lepinski




At 09:33 AM 11/8/2013, you wrote:

Hi Kirpal,

All Square D safety switches are UL tested in the Vertical position ONLY, so if 
someone is trying to install a switch in any other position other than 
vertical, that will be between them and the inspector.

Hope this helps. 

Eric
____________________________________________________________________________________

Eric Bentsen  |  Schneider Electric   |  Solar Business  |   UNITED STATES  |   
Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   Email: 
eric.bent...@schneider-electric.com  |  Site: www.schneider-electric.com/solar  
 |   Address: 250 South Vasco Rd., Livermore, CA 94551 


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to