Robin had a comment on the breaker issue...
I'll just copy and paste since he says it better than I can for this kind of stuff.
boB


Square D breakers are thermal breakers and are never used on PV combiners. I am not familiar with any solar applications where thermal breakers are used on a roof top. They would not be a good choice due to the high heat on a roof top. Square D thermal breakers are only rated for 50 volts DC anyway. The solar industry has always used CBI hydraulic/magnetic breakers up on the roof top for PV combiners. They come in 150 and 300VDC configurations. Some CBI breakers are also used for 600VDC disconnects up on the roof. Carling hydraulic/magnetic CX 600V breakers are also used up on the roof for disconnecting combiners. These breakers will change by about 5% for trip characteristics if laid on their back. Remember when you mount a breaker facing you and it is horizontal or vertical, this is still considered the vertical orientation because the front plane is vertical. PV combiners that use CBI breakers are made by OutBack and MidNite. There are over 2 million breakers in the field in all sorts of orientations. No problem with trip have ever been reported to me. That is a pretty good record. CBI breakers in the future will be non-polarized in accordance with NEC2014 so they can continue to be used in PV combiners.







On 11/11/2013 2:42 PM, Bill Hoffer wrote:
Dan

Hydraulic actuated breakers like the Classic Heiniman GJ,used in off grid battery based systems ( now made by Carlon and Airpax, since Henimans's patent ran out) it is very critical that they be used in the vertical position as is marked on the breaker's chassis. I know this from experience because I designed and got UL listed the GFI breaker ( common tripped GJ breakers with a .5 amp ground circuit, common today in many systems ) for Trace engineering and it kept failing the UL test for no apparent reason until we discovered the technician at UL was testing it on it's back, not in compliance with their own UL sticker on the device! Go figure.

But in support of Dan's comment, unless marked on the breaker itself, breaker operation is not dependent on orientation. Water proof rating of the enclosure is also another matter and the manufacturer should have specifics as to the mounting angle that keeps the outdoor rating. The angle can be very critical for any box that uses a lip to deflect water (NEMA 3R rating) rather than a seal to keep water out at any orientation (NEMA 4 or better). That is more of the issue here along with the fact that breakers are operating at less than ideal temperature ranges for the designed trip levels This would be relevant to the Square D disconnect that I am familiar with that uses an overlapping lip to get water spary out for it's 3R rating, if it was only tested in a vertical position than tiliting it would not be within the paramaters of the UL listing.
Bill


On Mon, Nov 11, 2013 at 9:21 AM, Exeltech <exelt...@yahoo.com <mailto:exelt...@yahoo.com>> wrote:

    Wrenches,

    There appears to be some misinformation getting into this thread.

    The "trip" mechanism within standard thermal over-current
    protective devices ("OCP devices") is mechanically spring-loaded,
    and is triggered by heat.

    Eric mentions below that Square D breakers are tested in a
    vertical orientation only - the implication being that's their
    only "UL certified" position.  If this were true, it would imply
    the breakers cannot be used in any other orientation.  This would
    potentially limit the Square D OCP market to sub-panels and other
    enclosures where the devices are vertical.  Inasmuch as the vast
    majority of panelboards I've encountered in my 40+ years in this
    industry have the breakers stacked horizontally, it would not be a
    wise business decision for the manufacturer to self-inflict such a
    limitation on their product.

    This also does not mean any such limitation (real or not) applies
    to all breakers.

    By way of example, OCP devices work in a horizontal position,
    stacked "pancake" style in a main panelboard, as well as
    vertically oriented side-by-side in a sub-panel.  In either
    orientation, they are  in full compliance with UL 489, (UL
    Standard for Circuit Breakers, Switches, and Circuit Breaker
    Enclosures).  If an OCP device *was* positionally-sensitive, UL
    Standards require this sensitivity to be noted in the
    documentation accompanying the device.  Further to that point, UL
    489 Section 7.1.1.13 states: "In determining if a circuit breaker
    complies with the test requirements, the device shall be mounted
    or supported as in service and tested under conditions
    approximating those of intended operation, except as otherwise noted."

    Mounting position notwithstanding, a greater concern would be the
    ambient temperature of a rooftop location, whereby summer heat
    would tend to make the OCP device more sensitive than necessary,
    potentially causing it to trip at an amperage below that of its UL
    ratings.  While a nuisance, a more serious issue arises when
    operating the OCP device in cold ambient conditions, whereby the
    device may allow MORE than its rated trip current to flow.

    Per UL 489, OCP devices are tested at either 25C or 40C ambient.
     Again per UL 489, if an OCP device is to be used in ambient
    conditions other than those two ranges, the acceptable temperature
    range for that OCP device shall be marked on the body of the device.

    In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3,
    mechanical vibration testing is conducted with OCP devices
    oriented vertically, horizontally, and inclined 30 degrees from
    vertical, with all devices energized up to 200% of the device
    rated current during the testing.

    Given the preceding, and per implication of UL 489 testing
    methods, OCP devices are NOT positionally sensitive.

    In conclusion, if you DO install a rooftop OCP system, and for
    proper protection, please ensure the OCP devices utilized are
    rated for the worst-case ambient temperatures involved.


    Regards to all,


    Dan Lepinski




    At 09:33 AM 11/8/2013, you wrote:

    Hi Kirpal,

    All Square D safety switches are UL tested in the Vertical
    position ONLY, so if someone is trying to install a switch in any
    other position other than vertical, that will be between them and
    the inspector.

    Hope this helps.

    Eric
    
____________________________________________________________________________________

    Eric Bentsen  |  Schneider Electric |  Solar Business  |   UNITED
    STATES  |   Technical Support Representative
    Phone: +(650) 351-8237 ext. 001#  |   Email:
    eric.bent...@schneider-electric.com
    <mailto:eric.bent...@schneider-electric.com>  |  Site:
    www.schneider-electric.com/solar
    <http://www.schneider-electric.com/solar>   |   Address: 250 South
    Vasco Rd., Livermore, CA 94551


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




--
Bill Hoffer
161 SE Fourth Ave
P.O. Box 1823
White Salmon, WA 98672
suneng...@gmail.com <mailto:bhof...@sunergyengineeringservices.com>



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to