Brian,


The requirement is generic. A listed contactor can meet the requirement. A 
standard is only necessary for products that want to be innovative in meeting 
the 30V, 240VA. Killing all power is an option with existing listed equipment. 
NEC 90.4 does not apply.



Bill.



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian Mehalic
Sent: Tuesday, January 21, 2014 2:36 PM
To: RE-wrenches
Cc: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown



It was suggested to me that since 690.12(5) requires the equipment to be listed 
and identified, and there is no standard for rapid shutdown equipment to be 
listed to then 90.3 (.4?...oh why isn't the NEC on my iPad...)says 'revert to 
the previous version of the NEC' and presto, no need to install rapid shutdown. 
I don't like this but the the person suggesting it certainly has an audience 
and this will appeal to installers looking to save on cost wherever possible.

Sent from my iPad


On Jan 21, 2014, at 5:11 PM, David Brearley 
<david.brear...@solarprofessional.com 
<mailto:david.brear...@solarprofessional.com> > wrote:

Drake,



The language in 690.12 is the compromise solution that was reached to ensure 
continued industry stability. The alternative to the combiner-level shutdown 
was module-level shutdown. It took a consolidated industry effort to push the 
module-level requirements out one more Code cycle—for the exact reasons that 
you touch on below.



Not sure if this link has been published on the Wrenches list or not, but it 
provides some background on the topic:



http://www.youtube.com/watch?v=sUXShMZJorQ



David Brearley

Senior Technical Editor, SolarPro magazine

NABCEP Certified PV Installation Professional

david.brear...@solarprofessional.com 
<mailto:david.brear...@solarprofessional.com>

Direct: 541.261.6545









On Jan 21, 2014, at 1:12 PM, re-wrenches-requ...@lists.re-wrenches.org 
<mailto:re-wrenches-requ...@lists.re-wrenches.org>  wrote:





From: Drake <drake.chamber...@redwoodalliance.org 
<mailto:drake.chamber...@redwoodalliance.org> >

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Date: January 21, 2014 11:36:15 AM CST

To: RE-wrenches <re-wrenches@lists.re-wrenches.org 
<mailto:re-wrenches@lists.re-wrenches.org> >

Reply-To: RE-wrenches <re-wrenches@lists.re-wrenches.org 
<mailto:re-wrenches@lists.re-wrenches.org> >




Bill,

It is good to see that energized conductors are going to be disconnected near 
the arrays. I've been an advocate of disconnecting these conductors by ground 
fault sensing equipment since ground fault detection was first implemented in 
the code. If contactors are to be installed on roofs, it likely won't be long 
before both ground faults and arc faults are automatically cleared.

When the requirement for AC arc fault branch circuit protection was first put 
in the NEC, it was postdated to allow time for the electrical industry to 
adapt. This new remote disconnecting requirement does not provide any lead time.

As the 2014 NEC is adopted in various jurisdictions, inspectors may feel that 
it is necessary to disallow systems without the newly required disconnect 
feature. This may result in serious problems for solar companies and customers, 
as well as manufacturers.

The protection of firefighters is essential. The implementation of renewables 
is essential also. Insurance claims for weather related, global 
warming-triggered climatic disasters are rising exponentially. Extreme weather 
related events result in major loss of life and billions of dollars in property 
damage. Atmospheric CO2 levels continue to climb from the burning of fossil 
fuels. This is a crisis of global proportions.

My request for code writers is to please take into account the effect that 
inserting new rules into the NEC may have on the stability of renewable energy, 
and implement new requirements in a way that will allow for a smooth interface.

Thank you,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>



---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to