OK. So I will have a high rate of acceptance if it buy an Tyco vacuum relay, and mount it in a Hoffman enclosure, and then put it on my roof?

On 1/21/2014 5:45 PM, Bill Brooks wrote:

Brian,

The requirement is generic. A listed contactor can meet the requirement. A standard is only necessary for products that want to be innovative in meeting the 30V, 240VA. Killing all power is an option with existing listed equipment. NEC 90.4 does not apply.

Bill.

*From:*re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Brian Mehalic
*Sent:* Tuesday, January 21, 2014 2:36 PM
*To:* RE-wrenches
*Cc:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

It was suggested to me that since 690.12(5) requires the equipment to be listed and identified, and there is no standard for rapid shutdown equipment to be listed to then 90.3 (.4?...oh why isn't the NEC on my iPad...)says 'revert to the previous version of the NEC' and presto, no need to install rapid shutdown. I don't like this but the the person suggesting it certainly has an audience and this will appeal to installers looking to save on cost wherever possible.

Sent from my iPad


On Jan 21, 2014, at 5:11 PM, David Brearley <david.brear...@solarprofessional.com <mailto:david.brear...@solarprofessional.com>> wrote:

    Drake,

    The language in 690.12 is the compromise solution that was reached
    to ensure continued industry stability. The alternative to the
    combiner-level shutdown was module-level shutdown. It took a
    consolidated industry effort to push the module-level requirements
    out one more Code cycle---for the exact reasons that you touch on
    below.

    Not sure if this link has been published on the Wrenches list or
    not, but it provides some background on the topic:

    http://www.youtube.com/watch?v=sUXShMZJorQ

    David Brearley

    Senior Technical Editor,/SolarPro/magazine

    NABCEP Certified PV Installation Professional

    david.brear...@solarprofessional.com
    <mailto:david.brear...@solarprofessional.com>

    Direct: 541.261.6545

    On Jan 21, 2014, at 1:12 PM,
    re-wrenches-requ...@lists.re-wrenches.org
    <mailto:re-wrenches-requ...@lists.re-wrenches.org> wrote:



        *From:*Drake <drake.chamber...@redwoodalliance.org
        <mailto:drake.chamber...@redwoodalliance.org>>

        *Subject:**Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*

        *Date:*January 21, 2014 11:36:15 AM CST

        *To:*RE-wrenches <re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>>

        *Reply-To:*RE-wrenches <re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>>




        Bill,

        It is good to see that energized conductors are going to be
        disconnected near the arrays. I've been an advocate of
        disconnecting these conductors by ground fault sensing
        equipment since ground fault detection was first implemented
        in the code. If contactors are to be installed on roofs, it
        likely won't be long before both ground faults and arc faults
        are automatically cleared.

        When the requirement for AC arc fault branch circuit
        protection was first put in the NEC, it was postdated to allow
        time for the electrical industry to adapt. This new remote
        disconnecting requirement does not provide any lead time.

        As the 2014 NEC is adopted in various jurisdictions,
        inspectors may feel that it is necessary to disallow systems
        without the newly required disconnect feature. This may result
        in serious problems for solar companies and customers, as well
        as manufacturers.

        The protection of firefighters is essential. The
        implementation of renewables is essential also. Insurance
        claims for weather related, global warming-triggered climatic
        disasters are rising exponentially. Extreme weather related
        events result in major loss of life and billions of dollars in
        property damage. Atmospheric CO2 levels continue to climb from
        the burning of fossil fuels. This is a crisis of global
        proportions.

        My request for code writers is to please take into account the
        effect that inserting new rules into the NEC may have on the
        stability of renewable energy, and implement new requirements
        in a way that will allow for a smooth interface.

        Thank you,

        Drake

        Drake Chamberlin
        /Athens Electric LLC//
        OH License 44810
        CO License 3773
        NABCEP Certified Solar PV
        740-448-7328
        /http://athens-electric.com/

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



------------------------------------------------------------------------
<http://www.avast.com/>   

This email is free from viruses and malware because avast! Antivirus <http://www.avast.com/> protection is active.




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to