NEC 2008, 240.21 (B)(1)(1) a.

Each of the smaller buss sections are feeders which are sized according to the tap rules. I believe the answer to your question is that the larger fuse can't protect the smaller buss. *But*, the likelihood of a short developing in that section of the circuit is very small and if one did, damage to the equipment would be limited that area. This is the essence of allowing taps.

Mark Frye

On 2/17/2015 6:17 AM, Allen Frishman wrote:Wrenchers,
I run into lots of Service Equipment that has a Large Service Switch which feeds multiple Sections with the Bus bar on each section rated significantly less than the main bus. A specific example that I am currently looking at has a 4000Amp Switch with a 3500 Amp Fuse which feeds 3 (1000 Amp) switchgear sections. How is it possible that the 3500 Amp Fuse protects the (3) 1000 Amp Sections? In this particular case each of the 1000 Amp Sections has between 3 and 6 fused switches on them. The sum of those switch/fuse ratings exceeds 1000 Amps in each case. For reference - This service gear is over 40 years old.

All thoughts are appreciated.

/Al Frishman/
AeonSolar

/(917) 699-6641 <tel:%28917%29%20699-6641> - cell/
/(888) 460-2867 <tel:%28888%29%20460-2867>/
/www.aeonsolar.com <http://www.aeonsolar.com/>/




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to