NEC 2011 - one inspectors misinterpretation of the code below for your amusement and comments. I have to admit that 705.12(D)(6) is somewhat ambiguous. Appropriate use of commas by code writers would be very helpful. I was able to find Mike Holt's guide that clears it up, so hopefully that will do the trick.
>From the inspector: I am sending this e-mail to straighten out the confusion and lay out the requirements of the 2011 NEC requirements which now govern solar photovoltaic breaker requirements. Any back fed breaker is required to be secured in accordance with 2011 NEC 408.36 (D) which says: *Back-Fed Devices.* Plug -in type overcurrent protection devices or plug in type main lug assemblies that are backfed and used to terminate field –installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel. This is also reiterated in the solar photovoltaic article 2011 NEC 690.10 (E) which says: *Back-fed Circuit Breakers.* Plug-in type back-fed circuit breakers connected to a stand-alone inverter output in either stand-alone or utility-interactive systems shall be secured in accordance with 408.36(D). Circuit breakers that are marked line or load shall not be backfed. *NEC 2011 Article* ** *705.12(D)(6) does not say what you have sent. This is what it says Word for Word:* *Fastening.* Listed plug-in type circuit breakers backfed from utility-interactive inverters that are listed and identified as interactive shall be permitted to omit the additional fastener normally required by 408.36(D) for such applications. What this article says is that if the manufacturer has gotten his breaker UL listed and the breaker is identified as interactive it may be used without a hold down device. Again in conclusion a breaker may be used if it has been certified and listed by the manufacturer and is marked interactive. If you can find a listed and interactive identified breaker then you may use it without having to secure it in place as required by 408.36(D). All parties involved have been sent the above attached document which very nicely explains the new requirements but I will attach it again just in case you happened to have lost it. If anyone has anymore questions please feel free to contact me.
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org