Hi Jason

I would see if your inverter company has an engineer that can send a letter or 
pay Bill B to write one. 
I don't see how you can get out of  his logic of yet another well written piece 
of code. 

Jay
Peltz power. 

Sent from my iPhone

> On Nov 18, 2015, at 5:29 AM, Jason Szumlanski 
> <ja...@floridasolardesigngroup.com> wrote:
> 
> This has reached a new level of misinterpretation. See my response and 
> inspector's further misinterpretation regarding fastening of breakers. I'm at 
> a loss of what to do now. I would just have the backfed breakers fastened, 
> but the clips can't be installed on adjacent breakers, so it's impossible 
> when you have more than one backfed breaker on one side of a panelboard.
> 
> Am I missing something here?
> 
> 
> 
> 
> 
> 
> On Wed, Nov 18, 2015 at 8:04 PM, Inspector Who Shall Not Be Named wrote:
> 
> Sorry I haven’t gotten back to you in a couple of days. 
>  
> 2011 NEC Article 690.10 (E) says:
>  
> Back-fed Circuit Breakers.  Plug-in type back-fed circuit breakers connected 
> to a stand-alone inverter output in either stand-alone or utility-interactive 
> systems shall be secured in accordance with 408.36(D).  Circuit breakers that 
> are marked line or load shall not be backfed.
>  
> It is stand a stand alone output if it is not fed back into the meter.  It is 
> a utility interactive output if it is.  But either way the inverter itself is 
> stand alone unit.
>  
>  
> 2011 NEC Article 705.12(D)(6) says:
>  
> Fastening.  Listed plug-in type circuit breakers backfed from 
> utility-interactive inverters that are listed and identified as interactive 
> shall be permitted to omit the additional fastener normally required by 
> 408.36(D) for such applications.
>  
> As you can see it says LISTED PLUG IN TYPE CIRCUIT BREAKERS.  It also says 
> listed for the inverter but is needed is a listed breaker or it needs to be a 
> bolt in type.
>  
> These are the new NEC changes that are now in effect.
> 
> 
> 
> 
> On Fri, Nov 13, 2015 at 4:24 PM, Jason Szumlanski <> wrote:
> I think there are two sources of confusion here.
>  
> 610.10(E) does not apply to the systems in question in any way. 610.10 
> applies only to breakers connected to a standalone inverter. The definition 
> of stand-alone system (690.2) is a system that operates independently of a 
> distribution network (utility). These systems are not stand-alone.
>  
> ​​705.12(D)(6) says the inverter needs to be listed and identified as 
> interactive, not the breaker.
> 
> 
> 
> 
>> On Fri, Nov 13, 2015 at 5:05 PM, Jason Szumlanski 
>> <ja...@floridasolardesigngroup.com> wrote:
>> NEC 2011 - one inspectors misinterpretation of the code below for your 
>> amusement and comments. I have to admit that 705.12(D)(6) is somewhat 
>> ambiguous. Appropriate use of commas by code writers would be very helpful. 
>> I was able to find Mike Holt's guide that clears it up, so hopefully that 
>> will do the trick.
>> 
>> 
>> From the inspector:
>> 
>> ​I am sending this e-mail to straighten out the confusion and lay out the 
>> requirements of the 2011 NEC requirements which now govern solar 
>> photovoltaic breaker requirements.
>>  
>> 
>> Any back fed breaker is required to be secured in accordance with 2011 NEC 
>> 408.36 (D) which says:
>> 
>>  
>> 
>> Back-Fed Devices.  Plug -in type overcurrent protection devices or plug in 
>> type main lug assemblies that are backfed and used to terminate field 
>> –installed ungrounded supply conductors shall be secured in place by an 
>> additional fastener that requires other than a pull to release the device 
>> from the mounting means on the panel.
>> 
>>  
>> 
>> This is also reiterated in the solar photovoltaic article 2011 NEC 690.10 
>> (E) which says:
>> 
>>  
>> 
>> Back-fed Circuit Breakers.  Plug-in type back-fed circuit breakers connected 
>> to a stand-alone inverter output in either stand-alone or 
>> utility-interactive systems shall be secured in accordance with 408.36(D).  
>> Circuit breakers that are marked line or load shall not be backfed.
>> 
>>  
>> 
>>  
>> 
>> NEC 2011 Article
>> 
>> ​​705.12(D)(6) does not say what you have sent.  This is what it says Word 
>> for Word:
>>  
>> 
>> Fastening.  Listed plug-in type circuit breakers backfed from 
>> utility-interactive inverters that are listed and identified as interactive 
>> shall be permitted to omit the additional fastener normally required by 
>> 408.36(D) for such applications.
>> 
>>  
>> 
>> What this article says is that if the manufacturer has gotten his breaker UL 
>> listed and the breaker is identified as interactive it may be used without a 
>> hold down device. 
>> 
>>  
>> 
>> Again in conclusion a breaker may be used if it has been certified and 
>> listed by the manufacturer and is marked interactive.  If you can find a 
>> listed and interactive identified breaker then you may use it without having 
>> to secure it in place as required by 408.36(D).  All parties involved have 
>> been sent the above attached document which very nicely explains the new 
>> requirements but I will attach it again just in case you happened to have 
>> lost it.
>> 
>>  
>> 
>> If anyone has anymore questions please feel free to contact me.
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to