Hi Carl,

Given that you are using SE equipment. I'm guessing that locking out the DC 
disco or AC side to shut the array down wasn't an option the inspector wanted?  

I thought that is one of the reasons for using SE?  

Jay
Peltz power. 

> On Jan 4, 2016, at 7:58 AM, Carl Adams <[email protected]> wrote:
> 
> Fellow Wrenches,
> 
> We recently failed an inspection on a new PV installation
> We are operating under the 2008 code
> I have attached a small sketch of our conduit routing to clarify things.
> 
> Inspectors note post inspection ...provide a photovoltaic disconnecting means 
> per 690.14 (C)(1) 
> 
> During his inspection the inspector was unhappy that we had entered the attic 
> space with the DC source circuits, saying we should have run the conduit 
> across the roof and kept it outside.  Since we entered the building we would 
> need to add a DC disconnect in the attic to meet code.  My thought is that we 
> fall under the exception listed (690.31(E)) since all source circuit internal 
> to the dwelling are in metallic raceways.  I'd like to hear other wrenches 
> chime in on this.
> 
> Our reason for routing things as we did was to keep the installation 
> aesthetics first class and minimize unsightly conduit runs.
> 
> Code section follows
> 
> 690.14 Additional Provisions. Photovoltaic disconnecting
> means shall comply with 690.14(A) through (D).690.14 
> 
> (C) Requirements for Disconnecting Means. Means
> shall be provided to disconnect all conductors in a building
> or other structure from the photovoltaic system conductors.
> (1) Location. The photovoltaic disconnecting means shall
> be installed at a readily accessible location either on the
> outside of a building or structure or inside nearest the point
> of entrance of the system conductors.
> Exception: Installations that comply with 690.31(E) shall
> be permitted to have the disconnecting means located remote
> from the point of entry of the system conductors.
> The photovoltaic system disconnecting means shall not
> be installed in bathrooms.
> 
>  690.31 (E) reads as follows
> (E) Direct-Current Photovoltaic Source and Output
> Circuits Inside a Building. Where direct-current photovoltaic
> source or output circuits of a utility-interactive inverter
> from a building-integrated or other photovoltaic system are
> run inside a building or structure, they shall be contained in
> metal raceways, or metal enclosures, from the point of penetration
> of the surface of the building or structure to the
> first readily accessible disconnecting means. The disconnecting
> means shall comply with 690.14(A) through (D).
> 
> 
> With Regards
> Carl Adams, President
> SunRock Solar, LLC
> 513.290.9072 (cell)
> 513.766.6025 (office)
> 
> <DC Source Conduit Run.pdf>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to